APC SRT2200XLI – Overcharging batteries (80V output, swollen batteries, burned connector)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SRT2200XLI – Overcharging batteries (80V output, swollen batteries, burned connector)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
ApertureSC
ApertureSC
Cadet

Posted: ‎2025-10-15 07:23 AM . Last Modified: ‎2025-10-15 09:21 AM

0 Likes
1
424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 07:23 AM . Last Modified: ‎2025-10-15 09:21 AM

APC SRT2200XLI – Overcharging batteries (80V output, swollen batteries, burned connector)

Hello everyone,

 

I have a question about my APC Smart-UPS SRT2200XLI.

I recently opened it after noticing problems with the battery pack.

 

Here’s the situation:

 

The UPS had been working normally for a long time.

 

All six internal 12 V 5 Ah batteries (LONG WP5-12) are now swollen, and one of the negative connectors is burned.

 

The inside of the UPS looks clean — no visible burn marks or damaged components.

 

Out of curiosity, I measured the voltage on the battery connector coming from the UPS, with no batteries connected, and I get around 80 V DC.

 

 

So my question is simple:

Is it normal for the SRT2200XLI to show around 80 V DC on the battery connector when no batteries are attached,

or does that indicate a problem with the charging circuit or voltage regulator?

 

Any help or confirmation from someone who has tested this model before would be really appreciated.

 

Thanks a lot!

– Esteban

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2025-10-16 05:30 AM

0 Likes
0
407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-16 05:30 AM

The SRT2200 is a 72 VDC battery system as such the float voltage would hover around (approximately) 78 VDC using 13 VDC as a reference.

 

Real world the individual cells would be 13.6 VDC for a floating pack voltage of 81.60 VDC.

 

Maximum (charging) voltage using the battery makers specification data sheet is 14.4 ~ 15.X VDC. Using the lower (maximum charging) voltage that would be 86.4 VDC.

 

I can tell by the battery name (Long) this specific RBC has been in place well past five years!

 

The average service life is 2-5 years based on usage, temperature, and environmental conditions.

 

The cells inside are rated to provide 260 full depletion cycles before signs of degradation.

 

If we ignore over charging as the root cause for now - still possible.


The fact the RBC internal cells are swollen indicates this unit has been cooking off for a very long time! 🤦‍♂️

 

Show me a photo of the serial number of the system and the production date sticker for the RBC that’s swollen. Along with the following logs in their entirety: Event, Data, UPS, Diagnostic.

 

Long branded cells haven’t been used in any APC UPS for years!

 

NOTE: DC Voltage measurements must be taken at the Anderson connector with and without the RBC connected.

 

As the DC voltage measured isn’t under load.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore