APC SRT1500XLA Fan keeps running

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SRT1500XLA Fan keeps running
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Thudo_apc
Crewman Thudo_apc
Crewman

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:09 AM

0 Likes
6
6095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:09 AM

APC SRT1500XLA Fan keeps running

Unlike previous APCs I have owned this one is a MUCH higher end model then all the others yet the fan on it never shuts off at all: its constantly on and driving me insane! It should be off especially when the power has not been interrupted or the trunks lines are off/unplugged.

Please tell me there is a way to curtail the fan and make this unit quiet like the others as the unit is nearby to my work desk (like all previous APCs I've owned) and can't have this constant droning sound. Thank you!

Since this is a new unit as of Feb/2019 it has 07.1 firmware.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

0 Likes
1
6090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

Hi,

To The UPS has a Smart slot so if you would like to manage over your network you can add a netowrk management card. The SKUs are AP9630, AP9631, or AP9635

As for the configuration, reset the UPS (see FAQ FA156611). If the reset / brain dead does not resolve the issue please contact local support at 800-555-2725 Option 1. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

0 Likes
0
6090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

Hi Ed

The SRT utilizes a fan that is always spinning, and just the speed of it changes depending on conditions like battery temperature, load, and input current.

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Thudo_apc
Crewman Thudo_apc
Crewman

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

0 Likes
0
6090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

Good morning Matt..

My load is so low right now (5%) that it shouldn't be running at all like previous models. 😞

Whatever happened to invoking the battery / voltage check when required like all previous APC's I've owned? Why have the fan on all the time when its not required unless power is disrupted OR voltage changes in the mains?

Reply

Link copied. Please paste this link to share this article on your social media post.

Thudo_apc
Crewman Thudo_apc
Crewman

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

0 Likes
0
6090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

Update..

The APC has been moved to another room with a heavy-duty extension code threaded through the ceilings/unfinished walls over to where the most critical units to have uninterrupted / clean power are stationed. Not entirely ideal but I can't have that 50dB noise droning on from the APC. I am disappointed this 1500XLA does not dynamically kick in the fan when required (mains are down or faulting voltage) like all other APCs in the past due but then again this is a much higher/industrial grade APC compared to others (since its also a rack-mount).

I gather there is no way this 1500XLA can connect via Ethernet to my Router but has to be managed via USB or Serial Con or hands-on digital display directly? The actual digital display gives me everything I need anyway.

Reply

Link copied. Please paste this link to share this article on your social media post.

Thudo_apc
Crewman Thudo_apc
Crewman

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

0 Likes
0
6090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

Sorry to bother but another question..

The SRT1500XLA seems to not save my commands (I am working off the unit's own digital display) where, for example, if I want to disable Green Mode OR turn back on audible sounds it says it made the change but then a few seconds later it reverts. 😐 Why?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

0 Likes
1
6091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:58 AM . Last Modified: β€Ž2024-03-15 06:08 AM

Hi,

To The UPS has a Smart slot so if you would like to manage over your network you can add a netowrk management card. The SKUs are AP9630, AP9631, or AP9635

As for the configuration, reset the UPS (see FAQ FA156611). If the reset / brain dead does not resolve the issue please contact local support at 800-555-2725 Option 1. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-10-29 11:14 AM

In response to BillP
0 Likes
0
5834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-10-29 11:14 AM

Just curious, what made the engineers decide to make this normal operation, these UPS's generate almost no heat when not on battery or charging and I get it, they are "drip charging" the battery at all times but that still generates little to no heat. I ended up having to get a refund on my SRT1500XLA because I can't have the noise in my office/family room, I was replacing a SMX1500RM2U that was old. I have since bought a SMX1500RM2U and just like my older unit this does not run the fan all the time.......Why did APC make this annoying decision to run the fan all the time on just the SRT and not SMX, is there a difference? they are both 1500.. Thanks in advance.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore