Symmerta PX Battery Temperatures and Cooling

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmerta PX Battery Temperatures and Cooling
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-06 08:48 AM . Last Modified: ‎2021-10-06 08:57 AM

0 Likes
6
3111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-06 08:48 AM . Last Modified: ‎2021-10-06 08:57 AM

Symmerta PX Battery Temperatures and Cooling

I'm examining a PX with 3-4 year old battery packs.  A few packs have reported failed in the last two months, and after removing, allowing time to cool and putting back in a different slot to verify the failure, they did not re-report failure.

 

Then when another one faulted, I took the time to open it up first, and discovered deformed SLA battery.  We've all seen melty batteries before, but I snapped a thermal pic that is just too cool not to share:

img_thermal_1633371787373(1).jpg

The white area is where it was bubbled out.  Glad I had my PPE on.  NFG at all, I do say.  PROTIP: If you need oven mits to remove a battery cartridge, it's bad.  I wonder if I can get an SE embroidered oven mit from a sales rep next time we order.

 

What cooling, if any, is the PX 80kva battery cabinet supposed to provide?  I don't feel any moving air, at all, around it so I was wondering if perhaps our fans had failed.

 

What is the nominal temperature range for battery packs? (Ours are all model SYBTU1-PLP )

 

I shot some video on a high res FLIR camera if you're interested.  Pardon my voice.  I was at a dentist 30 minutes prior.  The video shows temp on a color scale that updates each frame, but the key/scale is always present in the video,

 

video 1 (Whole battery cabinet)  video 2 (the culprit pack) 

 

 

I'd expect some temperature variation to always be present.  But just how much is normal?   +/- 10%  in celsius/kelvin/faren?  No doubt there's a problem with the pack I pulled.  But the pack on the bottom, only ten or so degrees above the others, is it worth pulling?

 

Labels
  • Labels:
  • Datacenter UPS
  • Rack Accessories & Cooling
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-19 02:53 PM

In response to ojfsdi
0 Likes
4
3046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-19 02:53 PM

Hi,

 

There is no "cooling" provided by the battery cabinet. There are perforations in the cabinet to allow for proper airflow. Generally speaking, the temperatures reported by the batteries in a PX80 are not much higher than the room ambient. 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-14 09:53 PM

0 Likes
5
3062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 09:53 PM

What cooling, if any, is the PX 80kva battery cabinet supposed to provide?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-19 02:53 PM

In response to ojfsdi
0 Likes
4
3047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-19 02:53 PM

Hi,

 

There is no "cooling" provided by the battery cabinet. There are perforations in the cabinet to allow for proper airflow. Generally speaking, the temperatures reported by the batteries in a PX80 are not much higher than the room ambient. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-20 08:16 PM

In response to al_buffington
0 Likes
3
3033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-20 08:16 PM

When they're sitting unused (tickle charging, I wouldn't expect the batteries to generate much heat.  But during discharge and charging they would, wouldn't they?

 

How much heating is normal?  I don't think the web interface displays the temp of every battery cartridge.  But I can see some variation on a FLIR camera at times.

 

The FLIR cam exentuates even the smallest variation, to about a tenth of a degree.  So I want to know what threshold I should be concerned about.  If one back is a degree F above its neighbors, should I replace it?  5 degrees?  10?

 

In this pic, you can see most of our packs are at 25C. But one is at 27.

img_thermal_1634774497341.jpg

the 27 degree one shows up as normal and OK in the management interface.

(sorry it's showing up sideways in this forum.  it's vertical on my pc.

 

The handles show up as lines in the flir image.  Also, Ignore the two vacant spots in L2 that show up hot.  that is an artifact of the reflective surface inside and FLIR imagery.  It's the same artifact that makes he handles show up btw.

 

But the elevated temp at position 4-C is not an artifact. 

 

How much heat, or variation in heat, is normal while not running on battery?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-25 05:45 AM

In response to ojfsdi
0 Likes
2
3004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 05:45 AM

Hi,

 

I've tried to address each of your questions below.

 

When they're sitting unused (tickle charging, I wouldn't expect the batteries to generate much heat. But during discharge and charging they would, wouldn't they? Yes, this is when the most heat is generated within the cabinet. The battery temp is always monitored though and they can have elevated temperatures while in normal operation. 

 


How much heating is normal? I don't think the web interface displays the temp of every battery cartridge. But I can see some variation on a FLIR camera at times. I'm not sure that I can answer what is "normal". It greatly depends on the environment where it's installed. The web interface does not display the battery temp. There should be a SNMP OID for the battery temperature, which on this system would show the module with the highest reading. FSRs, using their software tools, can read the individual battery module temp values 


The FLIR cam exentuates even the smallest variation, to about a tenth of a degree. So I want to know what threshold I should be concerned about. If one back is a degree F above its neighbors, should I replace it? 5 degrees? 10? There is no black and white answer to this. The UPS will not issue an alarm for an elevated battery temperature until a module reaches 40C. In addition, the UPS battery charger compensates for temperature. If you start to see a slightly lower float voltage on the batteries perhaps then you can be concerned as the charging to all of the batteries would be impacted. 



How much heat, or variation in heat, is normal while not running on battery? Again this will also depend on the environment. No studies have been done (to my knowledge) to examine temp variations within a system while in normal operation.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-27 07:39 PM

In response to al_buffington
0 Likes
1
2969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-27 07:39 PM

What does the charger do to compensate for temperature?

 

I'd imagine it reduces charging current if a pack is hot, but I don't want to put words in your mouth.  is that correct?

 

Is there a way to see and log over time the charging current being applied?

 

I know that I can observe voltage and current in and out of the UPS, so I suppose I could rig something up that would calculate total watts in and total watts out and the difference between that would be basically power to charge the batteries, right? 

 

Where can I get that software tool that can read temps of all modules?

 

I'd love to get that on our librenms graphs somehow.  I'd like to know if there is a reliable slow period of temperature growth before a pack goes temp critical and 'fails'

 

I'd gladly share the data I gather from monitoring the temp of all my cartridges over time.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-29 06:41 AM

In response to ojfsdi
0 Likes
0
2942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-29 06:41 AM

Hi,

 

I've tried to address each of your questions below....

 

What does the charger do to compensate for temperature? The battery float voltage is reduced. By how much will depend on how high the temperature is

 

Is there a way to see and log over time the charging current being applied? Not really. Although the charging current is visible through the software used by Field Service. 

 

I know that I can observe voltage and current in and out of the UPS, so I suppose I could rig something up that would calculate total watts in and total watts out and the difference between that would be basically power to charge the batteries, right?  I don't know if it would be that exact. I can tell you that each Power Module has a 1kw charger

 

Where can I get that software tool that can read temps of all modules? This is available only to internal Schneider Electric employees or authorized service providers. 

 

I'd like to know if there is a reliable slow period of temperature growth before a pack goes temp critical and 'fails' I don't believe such a study has been conducted.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore