APC SMX2200HV poor efficiency

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SMX2200HV poor efficiency
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:58 AM . Last Modified: ‎2024-03-15 06:08 AM

0 Likes
3
1558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:58 AM . Last Modified: ‎2024-03-15 06:08 AM

APC SMX2200HV poor efficiency

Dear all,

I recently got a SMX2200HV (230V) that now powers my office. The SMX series is advertised as a switch-mode unit that is basically a step-up from the SMT series (Features, extended runtime, efficiency).

These claims all match up very well for the smaller series up to 1500VA. However, the bigger models (SMX2200HV and SMX3000HV) seem to have a "poor" (i.e. significantly lower) efficiency in low-load scenarios according to the efficiency graph on the product website: https://www.apc.com/shop/uk/en/products/APC-Smart-UPS-X-2200VA-Rack-Tower-LCD-200-240V/P-SMX2200HV

For example, at 10% load the SMX2200HV has 85% efficiency. The SMX3000HV does a bit better, but I suspect they use the same circuit inside since at 200W load, both units exhibit 85% efficiency.

On the other hand, the smaller units have a much higher efficiency in low-load scenarios. For example, the SMX1500RMI2U has an efficiency of 92% (!) at 10% load - thats a 7% difference!

I would really be interested why that is, or if this is an error on the website.

Best regards,
Andreas

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

0 Likes
0
1557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

Correct. For best efficiency you would want to not oversize the UPS. That being said, none of these units is wildly inefficient, but obviously if you are talking about larger deployments (some customers have hundreds or even thousands of these units in use) it can certainly add up.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

0 Likes
0
1557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

Hi Andreas,

The SMT and SMX units are designed on different platforms and as such have different efficiency curves. SMX units can be used with additional external battery packs so they have larger chargers. You are correct that at low loads, the efficiency will be reduced. Personally I like to size these units so they will have about a 40-60% load attached. This will give you room for expansion if needed, but also keep things running efficiently. 

Hope this helps,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

0 Likes
0
1557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

Hi Lian,

thanks for your reply. My main concern however was that compared to smaller models of the SMX series, the larger models of the same series still have low efficiency at the same load percentage (e.g. 10%, which is 120W for the SMX1500 and 200W for the SMX2200).

Best regards, 

Andreas

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

0 Likes
0
1558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:59 AM . Last Modified: ‎2024-03-15 06:08 AM

Correct. For best efficiency you would want to not oversize the UPS. That being said, none of these units is wildly inefficient, but obviously if you are talking about larger deployments (some customers have hundreds or even thousands of these units in use) it can certainly add up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore