Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

APC SMART-UPS 450 change from 220V to 110V input-Line after battery change

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SMART-UPS 450 change from 220V to 110V input-Line after battery change
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
12
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

APC SMART-UPS 450 change from 220V to 110V input-Line after battery change

Hi.

I have an APC SMART-UPS 450 that works with 220V on input that is the line Voltage, the present line voltage supplied to the UPS system.

After the change of battery, the software PowerChute Business Edition show me that the Line Voltage and the Output Voltage is of 110V.

Is possible that some battery can change the behavior of the APC ups that works from 220V in input/output to 110V? Could that value be not real?

Thanks for your advice,

Mark

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 110v
  • 220v
  • apc
  • battery
  • change
  • ups
  • voltage
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

Hi

I have an APC SMART UPS RT 2000 .After replacing the battery is shows 110v in the HYPERTERMINAL as input voltage and the ups woldn't turn on.I get two error indications internal fault and overload red LED's are lighting up. I tried changing the values, but all i find are 105v,110v,120v,etc. I can't find 220v in the hyperterminal window. Please tell me how I can reset it back to 220v.

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

i am not sure how the UPS got to this state where it was corrupted. let me get those directions for you and PM them.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

I have the same issue, what are the Hyperterminal commands to change the voltage from 110 back to 220?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

Hi

I have an APC SMART UPS RT 2000 .After replacing the battery is shows 110v in the HYPERTERMINAL as input voltage and the ups woldn't turn on.I get two error indications internal fault and overload red LED's are lighting up. I tried changing the values, but all i find are 105v,110v,120v,etc. I can't find 220v in the hyperterminal window. Please tell me how I can reset it back to 220v.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

Hi,
i haven't done any changes before and after i physically replace the battery. I've only replace the battery.

This are the UPS Information Parameters:
- UPS Model SMART-UPS 450
- Firmware Revision 40.11.D
- Manufacture Date 21 dicembre 2000
- Serial Number NS0052231120
- Battery Replacement Date 12 2000
- UPS Identification UPS_IDEN

I attach the data log of the ups.

I've replaced the battery on 22/06/2012 at 10.31.28 a.m. and as you can see, after that, the values of input/output voltage have been changed.

Thanks for your advice,

Mark

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

i feel like i have heard of this before and it being some type of firmware corruption. did you do any changes before or physically after you replaced the battery? what does the model report as in the software?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

hi Mark,

I have an idea on what we can try but i won't be able to send you the instructions until later today via private message. i believe that we might be able to fix it. it'd require you to have the serial cable and a program like hyperterminal or putty to do terminal emulation with the UPS. i assume you have the serial cable since you are using powerchute but do you have a computer available with terminal emulation available?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

Hi,
the ups is connected via serial cable 940-0024C to a COM1 of a server with Windows 2003 Server installed.
Hyper Terminal is just installed on the operating system of the server.

Could you send me the instructions?

Is possible that the configuration inside the ups has changed after the change of battery?

Thanks a lot for helps,

Mark

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:43 AM

i am not sure how the UPS got to this state where it was corrupted. let me get those directions for you and PM them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

I have the same issue, what are the Hyperterminal commands to change the voltage from 110 back to 220?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

Hello,

We will find the UPSlink protocol information in Schneider Electric FAQ FA276164

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

Hi,  I only see one PDF, and it does not contain the info needed to change the voltage from 110V to 220V. It only contains the LICENSE AGREEMENT FOR UPS-LINKTM CONTROL LANGUAGE, see attached.

https://www.apc.com/shop/us/en/products/UPS-Link-Protocol-Language-Clicking-Download-confirms-you-ag...

 

Please advise.

Attachments
download (1).zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
2
6495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

Hi,

Sorry for the inconvenience. It appears the download link has been broken. I have attached a copy of the document.  Downloading the document confirms you agree to the License Agreement Terms. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

geoalf
geoalf
Cadet

Posted: ‎2024-12-08 01:02 AM

In response to BillP
0 Likes
0
3024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-08 01:02 AM

Hi. Did this problem solved? I think I have the same issue. it jumped to 120V. I think the firrware was corrupted

Could you help me with it

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

geoalf
geoalf
Cadet

Posted: ‎2024-12-08 01:05 AM

In response to BillP
0 Likes
0
3024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-08 01:05 AM

geoalf_0-1733648685772.png

And in web it shows two errors
2 Critical Alarms Present
Battery Charger Fault
System Configuration Fault

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore