I have UPS APC RT 10000VA/8000w. I check UPS status, I found there’s unacceptable utility voltage rate of change. That because the input voltage is 210.2VAC. This standard UPS power input is 220~240VAC. Please advice what is the effect of this low voltage rate? and how to deal with this case?
Please find attachment for more information. Thanks
Message was edited by: n4me
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:40 AM . Last Modified: 2024-03-14 12:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:40 AM . Last Modified: 2024-03-14 12:36 AM
I have UPS APC RT 10000VA/8000w. I check UPS status, I found there’s unacceptable utility voltage rate of change. That because the input voltage is 210.2VAC. This standard UPS power input is 220~240VAC. Please advice what is the effect of this low voltage rate? and how to deal with this case?
Please find attachment for more information. Thanks
Message was edited by: n4me
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:40 AM . Last Modified: 2024-03-14 12:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:40 AM . Last Modified: 2024-03-14 12:36 AM
Actually the electricity auto switch to power generator while power from municipal cut off. Really that the voltage 208 - 210VAC which're under 220vac wouldn't effect to any part of ups life?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:40 AM . Last Modified: 2024-03-14 12:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:40 AM . Last Modified: 2024-03-14 12:36 AM
I have UPS APC RT 10000VA/8000w. I check UPS status, I found there’s unacceptable utility voltage rate of change. That because the input voltage is 210.2VAC. This standard UPS power input is 220~240VAC. Please advice what is the effect of this low voltage rate? and how to deal with this case?
Please find attachment for more information. Thanks