Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC Modular Remote Power Panel 277 kVA and APC Modular Rack Distribution Panel 138kVA

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Modular Remote Power Panel 277 kVA and APC Modular Rack Distribution Panel 138kVA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:52 AM . Last Modified: ‎2024-03-19 12:31 AM

0 Likes
5
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:52 AM . Last Modified: ‎2024-03-19 12:31 AM

APC Modular Remote Power Panel 277 kVA and APC Modular Rack Distribution Panel 138kVA

Hi Folks,

Can anybody give me "Application Notes" or any 'learning material' so that I can understand the working mechanism of above captioned subject mentioned items. Like How they work? Why we need them.... etc....

thanks a lot.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

What would you like to know about them?

Take a look at this video: Breaker Demo - YouTube

The basic idea is when you install a new load (for example, a new rack with servers), ordinarily you need to hire an electrician to install a new electrical circuit to power the load. With the RPP (Remote Power Panel) or RDP (Rack Distribution Panel), you can buy a factory-produced "modular breaker" which is a circuit breaker attached to a cable (called a whip). The cable goes to the load and the circuit breaker hot-plugs into the touch-safe RPP or RDP. In that way you can provide a new electrical circuit without hiring an electrician. There are also subfeed hookups for electricians to hard-wire a circuit.

Additionally, the RPP and RDP monitors the electrical power used by every phase of every attached circuit. So if you like power monitoring, that can be useful.

The flip side is that modular breakers only come in specific configurations (see here). Some customers with esoteric needs cut the ends off the cable/whip and hardwire it themselves anyways, which isn't much benefit over conventional PDU panelboards.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

Hi Warifir,

I helped develop the RDP and RPP but I think it's best to talk to APC Sales Support if you want to install them. They have far more knowledge of installation concerns and can help determine if it's the right fit for you.

RDPs installed in racks (takes up 5U) while RPPs are themselves a half-width rack.

An RPP or RDP takes the place of a distribution board. Usually the input of the UPS is hard wired and the output is connected to the RDP/RPP. A modular breaker plugs into the RDP/RPP and the cable part of it goes to the load. The end of the modular breaker cable has a receptacle. Either the load equipment is plugged directly into this receptacle, or a PDU is plugged in (this is like a large surge strip) and the equipment is plugged into the PDU.

That setup assumes a large UPS powering multiple loads. We sell large UPSes with an attached RDP or RPP, such as the Symmetra PX All-in-one. In the picture for that product, you can see the modular breakers in an RDP at the very top of the rack.

Alternatively you may have many small UPSes powering your loads individually. In this case, you'd hard wire the input of an RDP or RPP, and then then plug the UPS inputs into the receptacle at the cable end of the modular breaker.

I hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

Hi Folks,

Can anybody give me "Application Notes" or any 'learning material' so that I can understand the working mechanism of above captioned subject mentioned items. Like How they work? Why we need them.... etc....

thanks a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

Do these help?

https://www.apc.com/prod_docs/results.cfm?DocType=Brochure&Query_Type=3&Value=432

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:31 AM

Thank u Angela for being so helpful, as always.

Your required link is valuable, but if you ever find anything in which "Working" details has mentioned then please let us know.

Thanks a lot for your prompt assistance. tc

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

What would you like to know about them?

Take a look at this video: Breaker Demo - YouTube

The basic idea is when you install a new load (for example, a new rack with servers), ordinarily you need to hire an electrician to install a new electrical circuit to power the load. With the RPP (Remote Power Panel) or RDP (Rack Distribution Panel), you can buy a factory-produced "modular breaker" which is a circuit breaker attached to a cable (called a whip). The cable goes to the load and the circuit breaker hot-plugs into the touch-safe RPP or RDP. In that way you can provide a new electrical circuit without hiring an electrician. There are also subfeed hookups for electricians to hard-wire a circuit.

Additionally, the RPP and RDP monitors the electrical power used by every phase of every attached circuit. So if you like power monitoring, that can be useful.

The flip side is that modular breakers only come in specific configurations (see here). Some customers with esoteric needs cut the ends off the cable/whip and hardwire it themselves anyways, which isn't much benefit over conventional PDU panelboards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore