APC Inrow Cooling Group Logics

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Inrow Cooling Group Logics
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
mrh7768
Crewman mrh7768
Crewman

Posted: ‎2022-11-28 07:43 AM . Last Modified: ‎2022-11-28 07:44 AM

0 Likes
4
2906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-28 07:43 AM . Last Modified: ‎2022-11-28 07:44 AM

APC Inrow Cooling Group Logics

Hi every one

 

I visited a site with 15 APC InRow cooling systems installed in 3 HACS. My question is the mode of operation and behavioral logic in the group of cooling systems. How does heating of a remote sensor of one inrow cause another system to increase fan speed and change its compressor capacity? How to choose an alternative system to compensate for more demand? How calculate demand? How to identify the problem created in a cooling system?
If there is a document that answers me, please post its link or file

 

Thank you for the possible response friends

Labels
  • Labels:
  • Datacenter Racks & Cooling
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-12-01 05:12 AM

2 Likes
3
2853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-01 05:12 AM

Hi @mrh7768,

 

Thank you for your question. There are a couple of things to cover in your question so I have addressed them separately below:

  • My question is the mode of operation and behavioral logic in the group of cooling systems. How does heating of a remote sensor of one InRow cause another system to increase fan speed and change its compressor capacity?
    • The cooling units use a direct expansion coil, a variable speed compressor to modulate refrigerant flow through the coil, and a set of fans to control airflow through the coil. In HACS mode the air flow in the room is controlled by enclosing the hot air aisle. The loads share an enclosed common hot aisle. Each unit in the containment controls their compressor ,EEV & fans independently based on their own supply temperature sensor reading. In a group configuration the supply temperature setpoint is shared among all the units, with each unit managing its own hardware based on its own supply temperature. Thus, there is no need for group control of the supply temperature. The fan speed is controlled by the fan speed preference setting. The fan speed can be selected based on the temperature differential across the cooling unit. As return temperatures deviate from the fan speed preference setting, the fan speed increases to bring the temperature difference back down to the setpoint or decreases fan output to increase the unit temperature differential. By maintaining the desired temperature differential, the system matches the airflow requirements of the load.

  • How to choose an alternative system to compensate for more demand?
    • With regards to compensating for an increased demand each unit has a operating range within it is effective. If the IT space has a higher demand than the current units are capable of meeting then additional units can be added to compensate. The issue more generally is when the thermal load is too low for the group of units. In this case there is the option of placing a number of units on Standby mode (dependent on the number of units installed vs the load). Note: Newer units have a “Load Assist” and “Runtime Balancing” functionality to address such a situation.
  • How calculate demand?
    • The cooling output is determined by the difference between the supply air temperature setpoint and the actual supply air temperature as well as the airflow (for each of the cooling units in the cooling group if more than one cooling unit is present).
  • How to identify the problem created in a cooling system?
    •  The firmware running on the controllers have a predefined list of alarm conditions with varying severity from alarm notices to shutdown commands for safety. This lists are long and specific to the model of unit and firmware revision. To give an example, if the pressure differential across the air filter pressure switch goes outside of a certain band then this will  appear as a change in voltage to the specific controller input. When the controller detects a voltage outside of the optimal range it will generate an alarm to check the air filter for debris or blockages. 
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mrh7768
Crewman mrh7768
Crewman

Posted: ‎2022-12-03 10:11 PM

In response to CiaranR
0 Likes
2
2819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-03 10:11 PM

Thank you very much for your reply. I am more looking for the logic of the cooling group. Let me put my question like this

1. In a cooling group (for example, 5 systems in a containment), is there a master/slave system that controls the performance status and capacity of the others?

2. In what case, one or more systems from a group increase the capacity for solve group problem? What causes the other coolers in the group to change fan speed or compressor capacity due to the identification of an issue in the group, even though they are in normal condition individually? Is there a problem or what causes it?

3. Is the placement of coolers in a group (physical location) important in group performance? If yes, how?

4. How is the concept of power required (demand) for the whole group determined? The output power of each cooling and the whole group is calculated based on what parameters?

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-12-07 04:58 AM

In response to mrh7768
0 Likes
1
2761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-07 04:58 AM

For grouped InRow (DX) based units ACRDxxx


Response for question 1,2 &4:
• Supply Air Control is handled by each unit independently of the group.
• InRow RD controls the Hot Gas Bypass Valve based on its own Supply Air PID
• Group member’s Fan Level is controlled by Master, based on master’s cooling PID
• All ACRD’s in the Group control to the same Rack Inlet Temperature for InRow Mode, or the average ∆T for HACS/RACS modes.
• All ACRD’s in the Group run at similar fan speeds.
• The ACRD will not support group control functions for Spot cooling mode.
• A Group will allow the user to configure the number of members within the Group. Maximum of 12.
• If the number of members discovered within the group is not equal to the configured number, a warning alarm informing the user of this condition will be issued.
• The Group Controller will ensure that Group configuration data items are consistent throughout all the customer interfaces in the Group
• The Group Controller will ensure the Group Status Data items are consistent throughout all customer interfaces in the Group.
• In the event of a conflict of Group configuration data items between members of the Group, the Group Controller’s data will supersede.
• The cooling demand is determined by the delta T between the supply air temperature (SAT) setpoint and the actual supply air temperature (RAT Rack Inlet) as well as the airflow for each of the cooling units in the cooling group.
• The controller varies fan speed trying to maintain the cooling setpoint. Fan speed min is 30%.
• When the cooling unit is programmed for Spot (Discrete), the fans run at a Fixed speed.

 

Response for question 3:
Yes, the placement of the units in an aisle is important to the performance. If the heated exhaust air is allowed to return to the air inlet of the equipment, an undesirable overheating condition may occur. Please refer to the links below for published Whitepapers exploring the effects of airflow management on cooling performance.

 

White Paper 44: Improving Rack Cooling Performance Using Airflow Management™ Blanking Panels

 

White Paper 50: Cooling Options for Rack Equipment with Side-to-Side Airflow

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mrh7768
Crewman mrh7768
Crewman

Posted: ‎2022-12-12 07:40 AM

In response to CiaranR
0 Likes
0
2743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-12 07:40 AM

Thanks for the links and full explanation
Regarding question 3, I meant the position of the cooling systems in relation to each other, and I did not mean the condition of the room.
For more explanation: In a room (hot or cold), there are 5 cooling systems. Placement is such that in a row of the cooling system, 1, 2 and 3 are next to each other and at a distance of one rack. System 4 and 5 are located in the opposite row with a distance of 3 racks between each other. If there is a crisis for system 1 and there is a need to increase the power of the group, on what basis does the system manage other cooling systems? How to recognize that system 3 and 5 are located in a place far away from system 1? Is there any control or setting on this placement? Should systems 2 and 4, which are close to system 1, compensate for the crisis of system 1 or the whole group? I mean prioritizing and maintaining balance in the group.
Thankful

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of