APC Device IP Configuration Wizard not finding NMC...

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Device IP Configuration Wizard not finding NMC...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:46 AM

0 Likes
5
4287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:46 AM

APC Device IP Configuration Wizard not finding NMC...

I've been setting up our APC NMC's over last couple of days and there is one APC NMC that will not get picked up by the wizard when it is searching. I've double checked the ethernet cable and placement in the switch. Getting green lights around the RJ-45 connector so everything looks good. Any ideas why it picked up the other 3 UPS systems but not this one? BTW, it is a Smart-UPS 2200 and the rest are Smart-UPS 3000's. Thanks for any help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
0
4287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

I've been setting up our APC NMC's over last couple of days and there is one APC NMC that will not get picked up by the wizard when it is searching. I've double checked the ethernet cable and placement in the switch. Getting green lights around the RJ-45 connector so everything looks good. Any ideas why it picked up the other 3 UPS systems but not this one? BTW, it is a Smart-UPS 2200 and the rest are Smart-UPS 3000's. Thanks for any help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:46 AM

0 Likes
0
4288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:46 AM

hi

unfortunately, this tool is not as reliable as you'd probably like so it could be a number of things.

1.) the tool works by looking for cards that are doing DHCP/BOOTP requests. if the card is not at a default state and boot mode of DHCP/BOOTP, the wizard will not find it.

2.) you mentioned green LEDs around the RJ-45 connector - i need to know exactly what you see for status LED - is it solid green, flashing green, alternating orange and green, etc - if its solid green, that indicates the card has valid IP settings and this wizard will definitely not work.

3.) if the card already got a DHCP or BOOTP address from your network, the card will also not pop up.

i would probably not waste time with this program to be honest and look towards another viable solution in [this knowledgebase article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3061]

hope that helps you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
0
4288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

Yeah I was curious of this program's efficiency. Yesterday when I was setting up the other NMC's, it was telling me that my IP's I was adding were in use when they have never been used before. I put the program on a different laptop and it didn't say that. Haha. Oh well.

Ok, it looks like the light on the right of the ethernet cable is a flashing green light while the left is solid orange. One problem I have with not using the wizard is that I don't know the MAC address of the UPS. It is in a series of 4 other systems so I can't access it on the box.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
0
4286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

i found out the other day that the only error message the program provides, no matter what the actual problem is, is "IP address already in use."

the program is going through drastic re-design in the future though.

i just want to make sure that you are looking at the jack correctly. does symbol near the solid left say 10/100 and the right hand side have a check mark or an X? just checking, depending on how you mounted the unit and are looking at it.

i think it will be ok for you to pull the card out hot, jot down the MAC, which starts with 00 C0 B&, and then insert the card back in there if you have no other solution.

if you have it mounted the way i think you do, it is telling us there are no valid IP settings on the card, with the flashing green status LED but I would just like to be sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
0
4286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

if it is an NMC1 (AP9617, AP9618, AP9619), yes you can with the APC serial cable - 940-0024 or 940-1524 - a standard serial cable will most likely cause a dropped load. the model of the card should be on the faceplate of it near the ethernet jack.

if its an NMC2 (AP9630, AP9631), the released version of the wizard won't work with it since the card is newer and the program wasnt designed to work with it.

a new version is due out shortly to correct that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
0
4288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:29 AM . Last Modified: ‎2024-03-14 12:45 AM

I've been setting up our APC NMC's over last couple of days and there is one APC NMC that will not get picked up by the wizard when it is searching. I've double checked the ethernet cable and placement in the switch. Getting green lights around the RJ-45 connector so everything looks good. Any ideas why it picked up the other 3 UPS systems but not this one? BTW, it is a Smart-UPS 2200 and the rest are Smart-UPS 3000's. Thanks for any help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore