Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

APC DLA1500L doesn't turn on

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: APC DLA1500L doesn't turn on
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
light767_apc
Ensign light767_apc
Ensign

Posted: ‎2021-07-07 10:54 PM

0 Likes
4
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 10:54 PM

APC DLA1500L doesn't turn on

This was originally posted on APC forums on 6/25/2015


Hi there!

I have just bought a used APC Smart UPS, model: DLA1500L; I have pluged it to the electricity but it doesn't turn on, all the front LED remain off. I have tried to push the 2 front buttons with no success. Probably the battery are exhausted but I was thinking that with the electricity online it would have turned on. I don't know if it's just broken ( so its circuit is broked ) or it doesn't power just because of exaust batteries. Any idea? 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
light767_apc
Ensign light767_apc
Ensign

Posted: ‎2021-07-07 10:55 PM

0 Likes
0
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 10:55 PM

This was originally posted on APC forums on 6/26/2015


Well actually the equipment is my desktop pc and all the stuff related ( Audio monitors, Video monitors, ink-jet printers) and I have bought this UPS in particolary because it has a pure sinusoidal output current instead of my old UPS which has an approximated one. My pc power supply is a high efficincy one and I have discovered recently that it could suffers with an approximated-sine wave UPS. So I have decided to buy a better UPS.

I have seen that this APC ups that I have bought is 3 or 4 years old, so the batteries could be dead for aging. I'll try to buy 2 new batteries and see.

By the way, eventually, if it's broken at circuit level ( I hope not..), it could be possible to repair it? I don't know what kind of circuit does it has (modern PCB or more classic circuit..).  

See Answer In Context

Reply
Share
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:54 PM

0 Likes
0
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 10:54 PM

This reply was originally posted by Bill on APC forums on 6/25/2015


Hi,

The unit will not power on if the batteries are dead. What is the battery voltage? You can check with a DC volt meter.

Reply
Share
light767_apc
Ensign light767_apc
Ensign

Posted: ‎2021-07-07 10:54 PM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 10:54 PM

This was originally posted on APC forums on 6/25/2015


I have tried to measure the voltage of each batteries and it even reach 1v... what if i leave the UPS pluged in on electricity?...any hope that it will recharge a little the batteries? I would like to be usre that the UPS doesn't turn on just because of the batteries before buy new ones. 

Reply
Share
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:54 PM

0 Likes
0
403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 10:54 PM

This was originally posted on APC forums on 6/26/2015


1V is well below the level at which the battery will be permanently damaged. You don't want to let them get below 9V, even for a brief time. Since the UPS won't turn on, it won't try to charge the batteries.

Since this is a used unit, you don't know if the batteries died because of a problem within the UPS, or if they died from old age and not being used. Normally I'd say something about deciding how important the equipment you want to connect to the UPS is, and then decide whether to try new batteries or a whole new UPS. Since you bought the UPS used, the equipment connected to it probably isn't that critical. You might want to try new batteries, but make sure you can return them if it turns out there is a problem in the UPS as well.

Reply
Share
light767_apc
Ensign light767_apc
Ensign

Posted: ‎2021-07-07 10:55 PM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-07 10:55 PM

This was originally posted on APC forums on 6/26/2015


Well actually the equipment is my desktop pc and all the stuff related ( Audio monitors, Video monitors, ink-jet printers) and I have bought this UPS in particolary because it has a pure sinusoidal output current instead of my old UPS which has an approximated one. My pc power supply is a high efficincy one and I have discovered recently that it could suffers with an approximated-sine wave UPS. So I have decided to buy a better UPS.

I have seen that this APC ups that I have bought is 3 or 4 years old, so the batteries could be dead for aging. I'll try to buy 2 new batteries and see.

By the way, eventually, if it's broken at circuit level ( I hope not..), it could be possible to repair it? I don't know what kind of circuit does it has (modern PCB or more classic circuit..).  

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc