Posted: 2024-05-16 01:40 PM
This worked fine for a few hours - then just randomly shut off - and will come back in about 5 minutes
?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-17 07:59 AM . Last Modified: 2024-05-17 08:00 AM
A few questions to answer and consider relating to your problem:
- What does the unit indicate is the last fault?
- What does the unit indicate is the current & percentage? Keeping in mind it should be below 80% 12 (amps).
- What is the unit defined for upper & lower voltage protection? What is the current voltage indicated by the unit now?
- Overload: Has the unit ever declared a overload and tripped the breaker?
Please answer all the questions listed above.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-21 04:12 PM
No faults indicated
5% 2.4 amps (approx)
92 Vols low 132 high
no overload - no tripper breaks
I tried the unit again yesterday - powers up - stays on - only now the only 2 left side lights on are POWER ON and LINE OK - the other 3 are not lit
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-22 01:25 AM
Based on your reply it sounds like the hardware is damaged / defective. You can try defaulting the unit through the menu. I don’t suspect it will make a difference though.
Is the unit plugged directly into the wall outlet?!? Do not use an extension or plug it into another SPD / UPS.
Let me know the above questions and the results. Failing that submit a RMA with APC Technical Support at this number as the unit has a lifetime warranty:
1-888-88APCAV
Please do let us know how everything turns out after the RMA process is completed. 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-22 06:03 AM
Yes tried a reset to default.
plugged directly into wall.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-23 07:00 AM
Contact APC Technical Support to submit a RMA for the unit. Have the serial number and receipt on hand so they can assist in the warranty repair / replacement.
Let us know how things turn out. 👍
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.