APC AP9605 PowerNet SNMP adapter serial connection issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC AP9605 PowerNet SNMP adapter serial connection issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-01-31 03:02 AM

0 Likes
2
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-01-31 03:02 AM

APC AP9605 PowerNet SNMP adapter serial connection issue

Hello,

I got this very old AP9605 SNMP card recently. I am fully aware that this device is 20 years old and that it has potential security issues. I have the quick start guide for it, but serial connection using the 2400bps, no parity, 8 data bits, 1 stop bit and no flow control setting did not work. After some trial and error, I found that using the same settings with 19200bps, upon pressing card reset, I get the following output:


*******************************
*        Initialization:      *
*  Default baud rate for the  *
*  Adapter's  SERIAL PORT 2   *
*  is 19200. To change it,    *
*  press CR. The Adapter will *
*  adjust to the baud rate of *
*  your console.              *
*******************************

Time out for baud rate auto detection


Your terminal Baud Rate is >19200<
American Power Conversion PowerNet SNMP Agent v2.2, Agent Loader v1.0
(c) Copyright 1992-1994 by American Power Conversion Corporation.
    All Rights Reserved.

-------- END OF OUTPUT -----------

Pressing ENTER (CR) doesn't do anything, apart from adjusting comm speed to that of the console's. After getting this output, I get nothing more, nor I can trigger any action over serial. Did this happen because someone tried to do firmware flash before and got the card wrecked in the process? Is there anything I can do to revive the current firmware? I absolutely need version 2.x for communication to work with second generation Smart UPS models (legacy hardware for educational purposes, like AP250, AP400, AP600, AP900, AP1250, AP2000), because the available newest 3.x firmware for this card removed support for those models.

EDIT: I forgot to mention that the card was manufactured in 1996 (guessing from serial number). The UPS used for testing is however NOT one of the second generation, but from the third generation instead (SU700INET). I am going to try it with one of the second generation models using an AP9600 external chassis. If you have any info to share until then, please do so.

Thanks in advance for any help!

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Sprinterfreak_apc
Crewman Sprinterfreak_apc
Crewman

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-02-14 10:14 PM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-02-14 10:14 PM

The green flashing status LED looks like as if the card is stuck in a boot loop.

Bad news: There is no official way to recover. I'm facing the same issue today and looking for a way to clone the EEPROMs from another card. Maybe this works. APC must have thought about this way too because the PROMs are socketed. (no soldering)

Edit:I successfully fixed my card by cloning the flash ICs from a working card.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-01-31 03:02 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-01-31 03:02 AM

Using this same card inside an AP9600 expansion chassis with a Smart-UPS 900 (2nd gen.) produced the same results as above. I had an another AP9605 card nearby, which did not work at all. That card completely refuses to communicate with the terminal, and the RX/TX led flashes like twice a second (with no ethernet cable plugged in). I suppose this is some sort of a failure signal.

Reply

Link copied. Please paste this link to share this article on your social media post.

Sprinterfreak_apc
Crewman Sprinterfreak_apc
Crewman

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-02-14 10:14 PM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:48 AM . Last Modified: ‎2024-02-14 10:14 PM

The green flashing status LED looks like as if the card is stuck in a boot loop.

Bad news: There is no official way to recover. I'm facing the same issue today and looking for a way to clone the EEPROMs from another card. Maybe this works. APC must have thought about this way too because the PROMs are socketed. (no soldering)

Edit:I successfully fixed my card by cloning the flash ICs from a working card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of