Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

New in row cooling requirements

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • New in row cooling requirements
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Hwasly_apc
Crewman Hwasly_apc
Crewman

Posted: ‎2021-07-09 04:48 AM

0 Likes
8
293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

New in row cooling requirements

This was originally posted on APC forums on 6/6/2018


Hi team, 

We have small datacenter with sensitive and high secure data and servers. Currently it is one row with 7 racks. Soon we will add another servers racks. The cooling system is HVAC which damaged some servers. I am willing to install in row cooling system from your products but I have some questions that I need your answers to provide our project management team to start purchasing and so on.

My questions are:

1- are your in row cooling products enough to cool the DC, so I can stop HVAC?

2-for redundancy, shall I get two units. Each row has one cooling unit?

3-do you have built in monitoring system, so I can monitor environment and getting alarms, also system for redundancy ?

4-what is the best unit which fits with our requirements, also it doesn't need complex installation (plug and play)?

5-Could you please provide me some links for the proposed products by you? 

Regards

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 7/10/2018


Hello. The items are there for the cooling system. They have the unit, the condenser and the leak sensor off the cooling units. For the rest of the equipment in the row, it is up to what you are looking for. I can tell you the cooling systems have the equipment that is needed but the rest of the row is outside of my expertise.

Thank you

See Answer In Context

Reply
Share
Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 6/7/2018


Hello Hus. Here are some recommendations for your questions.

1- are your in row cooling products enough to cool the DC, so I can stop HVAC?

A- This depends on the heat load in your room. We have a variety of different sized Inrow cooling units that can cool between 5kw-70KW of heat load per cooling unit.

2-for redundancy, shall I get two units. Each row has one cooling unit?

A-Most of our DX (air cooled) Inrow units can do lead/lag to allow a backup unit for redundancy. This will also depend on the setup of the room to determine how many units would be needed to have redundancy in the room.

3-do you have built in monitoring system, so I can monitor environment and getting alarms, also system for redundancy ?

A- All of our Inrow units come with a network card in them that allows network access to them for monitoring and alarm emails. They will just need to be hooked up to your network.

4-what is the best unit which fits with our requirements, also it doesn't need complex installation (plug and play)?

A-This will depend on your requirements for the Data center. Please see below for suggestion on getting help on sizing.

5-Could you please provide me some links for the proposed products by you?

A- Here is a link to our website for our cooling products.

http://www.apc.com/shop/us/en/categories/cooling/N-yp2yk2

I recommend calling into your local sales support as they can can walk you through the selection process to see which of the Inrow options will work best for your data center. The number can be found on our website under support tab and contact us. 

Thank you

Reply
Share
Hwasly_apc
Crewman Hwasly_apc
Crewman

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This was originally posted on APC forums on 6/7/2018


Thanks. Email has been sent. 

Reply
Share
Hwasly_apc
Crewman Hwasly_apc
Crewman

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This was originally posted on APC forums on 7/5/2018


Hi team. 

I have called your local supplier. Therfore, supplier sales manager have visited us, later he shared with us two designs including quotations. 

So, I believe that the cost is so high for small DC and there is a difference between quotations and your website. Can you help me to review designs and quotations? 

I would like to get an email for non local supplier otherwise can I  attach both design and quotation here?

Regards, 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 7/6/2018


Hello Hus.

We are tech support here so we do not deal with the pricing or design on new systems. We can take a look if you would like to post the designs but I am not sure how much we will be able to help on this side.

Thank you

Reply
Share
Hwasly_apc
Crewman Hwasly_apc
Crewman

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This was originally posted on APC forums on 7/6/2018


That's great if you can review the design and required parts. 

I have attached them. Please have a look and provide me your feedback. 

Thanks. 

Attachments
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 7/9/2018


Hello. The Layout looks good on the drawings. You will need to make sure you have enough heat load in the room for the 600mm units. They require at least 15 kw of heat load each to run properly (more heat load then this is better). As long as there is 15 kw of heat load, then you can run one unit and have two in back up, or if there is 30kw of load then you can run two and have one as a back up.

Thank you

Reply
Share
Hwasly_apc
Crewman Hwasly_apc
Crewman

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This was originally posted on APC forums on 7/9/2018


Thanks for your valuable feedback. 

Did you check the bill of materials? 

Are all items required except first item? 

Thanks again and BR  

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:48 AM

0 Likes
0
293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 04:48 AM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 7/10/2018


Hello. The items are there for the cooling system. They have the unit, the condenser and the leak sensor off the cooling units. For the rest of the equipment in the row, it is up to what you are looking for. I can tell you the cooling systems have the equipment that is needed but the rest of the row is outside of my expertise.

Thank you

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc