APC AP7723 ATS application failure after unsuccessful firmware uprade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC AP7723 ATS application failure after unsuccessful firmware uprade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:34 AM . Last Modified: ‎2024-02-15 12:14 AM

0 Likes
1
1907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:34 AM . Last Modified: ‎2024-02-15 12:14 AM

APC AP7723 ATS application failure after unsuccessful firmware uprade

I tried to upgrade the firmware on APC AP7723 from version 3.7.1 to the latest 3.9.2.

I used "apc_hw02_aos392_g2ats392.exe" utility for upgrade. It failed with OS transfer error, but here is the detailed result log: (A.B.C.D is the masked IP address of the device)

Starting Upgrade 08/15/18: 18:28:24    
-----------------
08/15/18: 18:28:24   A.B.C.D: Testing device connection
08/15/18: 18:28:25   A.B.C.D: Device connection passed
08/15/18: 18:28:26   A.B.C.D: Testing FTP Log-in
08/15/18: 18:28:30   A.B.C.D: FTP Log-in passed
08/15/18: 18:28:31   A.B.C.D: Saving data file
08/15/18: 18:28:46   A.B.C.D: AOS Prior to firmware transfer: Network Management Card AOS v3.7.4
08/15/18: 18:28:46   A.B.C.D: APP Prior to firmware transfer: Automatic Transfer Switch APP v3.7.1
08/15/18: 18:29:12   A.B.C.D: Saving event & configuration files
08/15/18: 18:29:21   A.B.C.D: Transferring OS
08/15/18: 18:31:17   A.B.C.D: ERROR --> OS transfer failed
Of course unloaded source was disconnected at that time when warning message appeared by the upgrade utility.
I found http://www.apc.com/ca/en/faqs/FA156178/ and tried to follow steps which described in NextGenRackATSg2atsUpgradeInstructions_V6.pdf 
The problem is that when I re-run the upgrade utility it drops "Incompatable HW". Here is the result log:
Starting Upgrade 08/23/18: 13:54:56    
-----------------
08/23/18: 13:54:56   A.B.C.D: Testing device connection
08/23/18: 13:54:56   A.B.C.D: Device connection passed
08/23/18: 13:54:57   A.B.C.D: Testing FTP Log-in
08/23/18: 13:55:01   A.B.C.D: FTP Log-in passed
08/23/18: 13:55:02   A.B.C.D: Saving data file
08/23/18: 13:55:02   A.B.C.D: Information --> Unable to verify previous version 
08/23/18: 13:55:03   A.B.C.D: ERROR --> Incompatable HW
08/23/18: 13:55:03   A.B.C.D: Incompatable HW: apc_hw02_aos_392.bin
08/23/18: 13:55:03   A.B.C.D: Incompatable HW: sec/

Right now device is available only thru telnet. Web interface reports:

g2sh5FQU0hzuMsHVYBkugA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngg2sh5FQU0hzuMsHVYBkugA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Here are the device information from telnet:
American Power Conversion               Network Management Card AOS      v3.9.2
(c) Copyright 2009 All Rights Reserved
-------------------------------------------------------------------------------
Name      : Unknown                                   Date : 08/23/2018
Contact   : Unknown                                   Time : 11:43:42
Location  : Unknown                                   User : Administrator
Up Time   : 7 Days 19 Hours 9 Minutes                 Stat : P+ N+ A-

        -----------------------------------------------------------------------
        About System
        Model Number      : AP7723
        Serial Number     : 5A1622T5XXXX
        Manufacture Date  : 06/01/2016
        Hardware Revision : 01
        MAC Address       : 00 C0 B7 F3 XX XX
        Flash Type        : AMD A29DL322DB
        Press to continue...
        -----------------------------------------------------------------------
        Module Information
        Description : Network Management Card AOS
        -----------------------------------------------------------------------
        Name        : aos               Type        : APC OS
        Version     : 392               Sector      : 16
        Date        : 07/06/2016        Time        : 15:12:05
        CRC16       : C3FF
        Press to continue...
        Description : Network Management Card AOS
        -----------------------------------------------------------------------
        Name        : aos               Type        : APC OS
        Version     : 392               Sector      : 47
        Date        : 07/06/2016        Time        : 15:12:05
        CRC16       : C3FF

Is there any idea to get back the into operation? At the moment there is no load on the device but it is not physically reachable to me.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:34 AM . Last Modified: ‎2024-02-15 12:14 AM

0 Likes
0
1905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:34 AM . Last Modified: ‎2024-02-15 12:14 AM

I would refer to NMC1 instructions here (http://www.apc.com/us/en/faqs/FA156047) for the manual FTP method and then find the apc_hw02_g2ats_392.bin file you should have that was extracted from the .exe file you downloaded started with. FTP (put) that file on the ATS and see if it fixes it.

Make sure to refer to the PDF you found because once you load that app file, the Network Management Card will likely have to push a controller update to the ATS which is where you'll see 'do' and 'co' explained in the document if can see the front of the UPS (but you did say you're not physically near it). What I mean is, load this g2ats .bin file over FTP and then give the ATS 5-10 minutes to fully recover and update before you do anything to it and start logging in, etc.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:34 AM . Last Modified: ‎2024-02-15 12:14 AM

0 Likes
0
1906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:34 AM . Last Modified: ‎2024-02-15 12:14 AM

I would refer to NMC1 instructions here (http://www.apc.com/us/en/faqs/FA156047) for the manual FTP method and then find the apc_hw02_g2ats_392.bin file you should have that was extracted from the .exe file you downloaded started with. FTP (put) that file on the ATS and see if it fixes it.

Make sure to refer to the PDF you found because once you load that app file, the Network Management Card will likely have to push a controller update to the ATS which is where you'll see 'do' and 'co' explained in the document if can see the front of the UPS (but you did say you're not physically near it). What I mean is, load this g2ats .bin file over FTP and then give the ATS 5-10 minutes to fully recover and update before you do anything to it and start logging in, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore