Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

APC AP7723 ATS application failure after unsuccessful firmware uprade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC AP7723 ATS application failure after unsuccessful firmware uprade
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:34 AM

0 Likes
1
478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:34 AM

APC AP7723 ATS application failure after unsuccessful firmware uprade

This question was originally posted by Mate on APC forums on 8/23/2018


I tried to upgrade the firmware on APC AP7723 from version 3.7.1 to the latest 3.9.2.

I used "apc_hw02_aos392_g2ats392.exe" utility for upgrade. It failed with OS transfer error, but here is the detailed result log: (A.B.C.D is the masked IP address of the device)

Starting Upgrade 08/15/18: 18:28:24    
-----------------
08/15/18: 18:28:24   A.B.C.D: Testing device connection
08/15/18: 18:28:25   A.B.C.D: Device connection passed
08/15/18: 18:28:26   A.B.C.D: Testing FTP Log-in
08/15/18: 18:28:30   A.B.C.D: FTP Log-in passed
08/15/18: 18:28:31   A.B.C.D: Saving data file
08/15/18: 18:28:46   A.B.C.D: AOS Prior to firmware transfer: Network Management Card AOS v3.7.4
08/15/18: 18:28:46   A.B.C.D: APP Prior to firmware transfer: Automatic Transfer Switch APP v3.7.1
08/15/18: 18:29:12   A.B.C.D: Saving event & configuration files
08/15/18: 18:29:21   A.B.C.D: Transferring OS
08/15/18: 18:31:17   A.B.C.D: ERROR --> OS transfer failed
Of course unloaded source was disconnected at that time when warning message appeared by the upgrade utility.
I found http://www.apc.com/ca/en/faqs/FA156178/ and tried to follow steps which described in NextGenRackATSg2atsUpgradeInstructions_V6.pdf 
The problem is that when I re-run the upgrade utility it drops "Incompatable HW". Here is the result log:
Starting Upgrade 08/23/18: 13:54:56    
-----------------
08/23/18: 13:54:56   A.B.C.D: Testing device connection
08/23/18: 13:54:56   A.B.C.D: Device connection passed
08/23/18: 13:54:57   A.B.C.D: Testing FTP Log-in
08/23/18: 13:55:01   A.B.C.D: FTP Log-in passed
08/23/18: 13:55:02   A.B.C.D: Saving data file
08/23/18: 13:55:02   A.B.C.D: Information --> Unable to verify previous version 
08/23/18: 13:55:03   A.B.C.D: ERROR --> Incompatable HW
08/23/18: 13:55:03   A.B.C.D: Incompatable HW: apc_hw02_aos_392.bin
08/23/18: 13:55:03   A.B.C.D: Incompatable HW: sec/

Right now device is available only thru telnet. Web interface reports:
Here are the device information from telnet:
American Power Conversion               Network Management Card AOS      v3.9.2
(c) Copyright 2009 All Rights Reserved
-------------------------------------------------------------------------------
Name      : Unknown                                   Date : 08/23/2018
Contact   : Unknown                                   Time : 11:43:42
Location  : Unknown                                   User : Administrator
Up Time   : 7 Days 19 Hours 9 Minutes                 Stat : P+ N+ A-

        -----------------------------------------------------------------------
        About System
        Model Number      : AP7723
        Serial Number     : 5A1622T5XXXX
        Manufacture Date  : 06/01/2016
        Hardware Revision : 01
        MAC Address       : 00 C0 B7 F3 XX XX
        Flash Type        : AMD A29DL322DB
        Press to continue...
        -----------------------------------------------------------------------
        Module Information
        Description : Network Management Card AOS
        -----------------------------------------------------------------------
        Name        : aos               Type        : APC OS
        Version     : 392               Sector      : 16
        Date        : 07/06/2016        Time        : 15:12:05
        CRC16       : C3FF
        Press to continue...
        Description : Network Management Card AOS
        -----------------------------------------------------------------------
        Name        : aos               Type        : APC OS
        Version     : 392               Sector      : 47
        Date        : 07/06/2016        Time        : 15:12:05
        CRC16       : C3FF

Is there any idea to get back the into operation? At the moment there is no load on the device but it is not physically reachable to me.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:34 AM

0 Likes
0
476
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:34 AM

This reply was originally posted by Angela on APC forums on 8/23/2018


I would refer to NMC1 instructions here (http://www.apc.com/us/en/faqs/FA156047) for the manual FTP method and then find the apc_hw02_g2ats_392.bin file you should have that was extracted from the .exe file you downloaded started with. FTP (put) that file on the ATS and see if it fixes it.

Make sure to refer to the PDF you found because once you load that app file, the Network Management Card will likely have to push a controller update to the ATS which is where you'll see 'do' and 'co' explained in the document if can see the front of the UPS (but you did say you're not physically near it). What I mean is, load this g2ats .bin file over FTP and then give the ATS 5-10 minutes to fully recover and update before you do anything to it and start logging in, etc.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:34 AM

0 Likes
0
477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:34 AM

This reply was originally posted by Angela on APC forums on 8/23/2018


I would refer to NMC1 instructions here (http://www.apc.com/us/en/faqs/FA156047) for the manual FTP method and then find the apc_hw02_g2ats_392.bin file you should have that was extracted from the .exe file you downloaded started with. FTP (put) that file on the ATS and see if it fixes it.

Make sure to refer to the PDF you found because once you load that app file, the Network Management Card will likely have to push a controller update to the ATS which is where you'll see 'do' and 'co' explained in the document if can see the front of the UPS (but you did say you're not physically near it). What I mean is, load this g2ats .bin file over FTP and then give the ATS 5-10 minutes to fully recover and update before you do anything to it and start logging in, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc