Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

APC 1500 PRO - Powerchute Business - failed to apply configuration

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 1500 PRO - Powerchute Business - failed to apply configuration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
12
402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

APC 1500 PRO - Powerchute Business - failed to apply configuration

This question was originally posted by Pablo on APC forums on 11/7/2013


Windows Server 2012

Powerchute Business agent/server/console in the same server

USB connected directly

Windows detects the UPS

in device list configuration im gettin failed to apply configuration profile

how can i fix it?

thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:38 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:38 AM

This reply was originally posted by Bill on APC forums on 11/22/2013


Hi,

When you open the PowerChute web interface https://127.0.0.1:6547 or https://server IP:6547 and it reports Device Communications not Established then the PBEServer will not be able to discover the device and you will see the error "failed to apply configuration profile". If the web interface does display the UPS information then the most common cause of your issue is the user name and password do not match for the Agent and the Server. Knowledge base document FA159590 discusses "failed to apply configuration profile"


Also, as Angela wrote if the UPS is a Back-UPS Pro 1500 PowerChute Business Edition Agent will not discover the UPS. With a Back-UPS Pro you should install PowerChute Personal Edition. Other software options are Windows Power Options in the control panel or APCUPSD.

See Answer In Context

Reply
Share
Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

This reply was originally posted by Pablo on APC forums on 11/7/2013


Windows Server 2012

Powerchute Business agent/server/console in the same server

USB connected directly

Windows detects the UPS

in device list configuration im gettin failed to apply configuration profile

how can i fix it?

thanks

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

This reply was originally posted by Pablo on APC forums on 11/7/2013


Ok, i founded...

this is my error

If the system where the Agent is installed has more than 1 network card, the

PowerChute Business Edition Server may not be able to locate the Agent. If this

is the case, check TCP/IP properties for it's binding order. Make sure the IP of

the card you are adding to the configuration is the first item in the TCP/IP

binding order.

the server 2012 has 2 nic cards in team mode.

server/agent/console are on the same server

how can i fix it?

thanks

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

This reply was originally posted by Angela on APC forums on 11/7/2013


Within Windows, you need to verify the binding order of your NICs. PowerChute Business Edition will use the first one.


These instructions may help -> http://technet.microsoft.com/en-us/library/cc732472(v=ws.10).aspx

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

This reply was originally posted by Pablo on APC forums on 11/10/2013


Mi list is:

vEthernet

Team

nic 1

nic 2

nics, are both phisycal network cards.

they both works in team and thats how vethernet is where i set up my IP v4.

IP are disabled in nic1, nic 2 and team

i only have 1 ip working in this pc

disable, firewall, antivirus, and still cant get my configuration to apply..

any ideas?

thanks

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

This reply was originally posted by Bill on APC forums on 11/11/2013


Hi,

Open a web browser on the system running the agent, server, and console and enter https://127.0.0.1:6547 to verify the Agent is accessible. If it is open the Console click on Tools - Device List and add 127.0.0.1

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

This reply was originally posted by Pablo on APC forums on 11/11/2013


i can open the agent via web browser but im getting this error

     
Device CommunicationsNot Established

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:37 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:37 AM

This reply was originally posted by Pablo on APC forums on 11/12/2013


anything to do?

i cant get it to work

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:38 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:38 AM

This reply was originally posted by Bill on APC forums on 11/12/2013


Hi,

Please enable 1 of the physical NICs with an IP v4 address, uninstall PCBE Agent and reinstall allowing the software to auto discover the UPS. If the software auto discovers then check the web interface again to verify that the UPS is communicating with the Agent.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:38 AM

0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:38 AM

This reply was originally posted by Pablo on APC forums on 11/13/2013


i will try it.

anyway, agent is auto discovering the UPS in the 192.168.x.x (the same computer where the server is installed) or in 127.0.0.1.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:38 AM

0 Likes
0
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:38 AM

This reply was originally posted by Pablo on APC forums on 11/22/2013


Cant get the PCBE to work

Then i intalled server/Agent on a Windows 7 sistema and still not working

im getting "failed to apply the configuration profile"

updated java, disabled firewall and antivirus.

whats wrong?

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:38 AM

0 Likes
0
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:38 AM

This reply was originally posted by Angela on APC forums on 11/22/2013


Maybe I missed this in the beginning but is this a Back UPS? PowerChute Business Edition does not work with Back UPS products via USB. You can verify the part number of the UPS on the back or bottom of it.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:38 AM

0 Likes
0
402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:38 AM

This reply was originally posted by Bill on APC forums on 11/22/2013


Hi,

When you open the PowerChute web interface https://127.0.0.1:6547 or https://server IP:6547 and it reports Device Communications not Established then the PBEServer will not be able to discover the device and you will see the error "failed to apply configuration profile". If the web interface does display the UPS information then the most common cause of your issue is the user name and password do not match for the Agent and the Server. Knowledge base document FA159590 discusses "failed to apply configuration profile"


Also, as Angela wrote if the UPS is a Back-UPS Pro 1500 PowerChute Business Edition Agent will not discover the UPS. With a Back-UPS Pro you should install PowerChute Personal Edition. Other software options are Windows Power Options in the control panel or APCUPSD.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc