Posted: 2025-03-18 04:27 PM
Has any official testing been conducted to confirm whether the Ethernet port complies with the 802.3 standard?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-09 01:29 AM
Hello,
The standards that complies for this card are shown below for immunity and emission :
FCC Class A, EN 61000-6-3, BS EN
61000-6-3, ICES-003 Class A, VCCI Class A,
AS/NZS, EN 55032 Class A, BS EN 55032
Class A
EN 55024, BS EN 55024, EN 61000-4-2, BS
EN 61000-4-2, EN 61000-4-3, BS EN
61000-4-3, EN 61000-4-4, BS EN 61000-4-4,
EN 61000-4-5, BS EN 61000-4-5, EN
61000-4-6, BS EN 61000-4-6, EN 61000-4-8,
BS EN 61000-4-8, EN 61000-4-11, BS EN
61000-4-11, EN 55035, BS EN 55035, EN
62040-2, BS EN 62040-2, EN 61326-2, BS
EN 61326-2
please refer to the attachment
This card compliant with cybersecurity standards as shown below
That is the official compliance available for this NMC card
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-09 01:29 AM
Hello,
The standards that complies for this card are shown below for immunity and emission :
FCC Class A, EN 61000-6-3, BS EN
61000-6-3, ICES-003 Class A, VCCI Class A,
AS/NZS, EN 55032 Class A, BS EN 55032
Class A
EN 55024, BS EN 55024, EN 61000-4-2, BS
EN 61000-4-2, EN 61000-4-3, BS EN
61000-4-3, EN 61000-4-4, BS EN 61000-4-4,
EN 61000-4-5, BS EN 61000-4-5, EN
61000-4-6, BS EN 61000-4-6, EN 61000-4-8,
BS EN 61000-4-8, EN 61000-4-11, BS EN
61000-4-11, EN 55035, BS EN 55035, EN
62040-2, BS EN 62040-2, EN 61326-2, BS
EN 61326-2
please refer to the attachment
This card compliant with cybersecurity standards as shown below
That is the official compliance available for this NMC card
Regards,
Karim