AP9631 refuses to reset

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 refuses to reset
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Murray_GGP
Murray_GGP
Cadet

Posted: ‎2022-09-26 04:06 AM . Last Modified: ‎2022-09-26 04:48 AM

0 Likes
2
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-26 04:06 AM . Last Modified: ‎2022-09-26 04:48 AM

AP9631 refuses to reset

Hi

 

We recently picked up a "preloved" SmartUPS 1500 that came with an AP9631; the seller warned me that the AP "has the latest firmware, but needs a factory reset", to which I was not overly concerned, having done a quick web search beforehand to get the (numerous) procedures.

 

However, while the SmartUPS is working "just fine", I cannot for the life of me get the AP9631 to factory reset; pushing the reset button in any number of ways does nothing to the status LED on the card. I've tried:

 

* The SE published steps (serial cable, hold in the reset button for 5-7 seconds, wait for the light to change, press the reset button again, hit enter in your serial terminal)

* The "internet favourite" hold in the reset button for at least a minute until the light changes

* Just a quick touch of the reset button to get it to go amber/flash/change in some way at all

 

Both with and without a(n active) network cable plugged in. Nothing works, the status light stays stubbornly green. The card appears to be otherwise working; I can get to the authentication via serial or web browser (thank the stars the UPS has a screen that told me the IP), and used a multimeter to "buzz out" the reset switch, so I know that is "alive", but without a reset mechanism I am stuck with whatever the previous authentication details are, and I can't modify the IP either.

 

Any advice on how to proceed?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-09-27 11:59 PM

0 Likes
1
1498
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-27 11:59 PM

Hi @Murray_GGP 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. I am sorry to hear about the issue that you are having with the AP9631, you can try the procedures outlined in the FAQ that I have provided below.

 

Using Network Management Card 2 (NMC2) bootmonitor to recover/upgrade firmware 

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-09-27 11:59 PM

0 Likes
1
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-27 11:59 PM

Hi @Murray_GGP 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. I am sorry to hear about the issue that you are having with the AP9631, you can try the procedures outlined in the FAQ that I have provided below.

 

Using Network Management Card 2 (NMC2) bootmonitor to recover/upgrade firmware 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Murray_GGP
Murray_GGP
Cadet

Posted: ‎2022-09-30 07:45 AM

In response to JonPro
0 Likes
0
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-30 07:45 AM

Hi JonPro,

 

Apologies for the delay in responding, I only go to my employers office (where this unit is) once a week, but otherwise many thanks; following the BootMonitor process (and factory_reset) has allowed me to get the card to permit login with apc/apc (and that's good enough for me for the present).

 

I'll now be able to assign a suitable IP for the network and use it for it's intended purpose.

 

Have "Marked as solution".

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore