unable to register NMC with PowerChute appliance

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • unable to register NMC with PowerChute appliance
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
scottmlew_apc
Ensign scottmlew_apc
Ensign

Posted: β€Ž2022-08-08 06:17 PM

0 Likes
8
2625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-08 06:17 PM

unable to register NMC with PowerChute appliance

I have an AP9631 running the latest firmware (AOS 7.0.8 and bootmon 1.0.9) and am trying to setup the PowerChute appliance with my vCenter server. The appliance is also the latest (v4.4.3). When the registration process occurs, it just displays a waiting cursor, then eventually times out. When I click the "fix issues" button, it brings me to the login screen, and then my login never completes and I get a 500. Both the NMC and the PC VM are on the same subnet, and I do see the UDP port 3052 broadcasts. I have tried deploying the appliance multiple times and even format'd the NMC to start over. I am sure I have matching credentials on both. I even tried the manual registration process mentioned in a forum post, but when I log in to the appliance, I just get a spinning cursor and the page never loads. I've also tried disabling firewalld on the appliance. I've attached the 2 config files. I'd appreciate any suggestions as to what may be wrong.

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2022-08-11 01:06 PM

0 Likes
7
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-11 01:06 PM

@scottmlew_apc 

 

The PCNS VM and vCenter are on network segment 10.0.60.x

pcns_host = 10.0.60.10
vCenter Server = 10.0.60.200

 

The NMC is on segment 10.0.40.x with a subnet mask of 255.255.255.0

[NetworkTCP/IP]
SystemIP=10.0.40.150
SubnetMask=255.255.255.0
DefaultGateway=10.0.40.1

 

The current registered PCNS clients are

[PowerChute]
CurrentPCNSClientIP1=10.0.40.10

 So the NMC will UDP packets to 10.0.40.255

 

To register the PCNS VM I recommend you change it and vCenter to the 10.0.40.x segment and verify the subnet mask and gateway match. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

scottmlew_apc
Ensign scottmlew_apc
Ensign

Posted: β€Ž2022-08-11 01:18 PM

In response to BillP
0 Likes
6
2567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-11 01:18 PM

@BillP 

 

Thanks very much for your reply. That is a good catch about the PCNS IP -- I admit I had missed that in the config file.

 

However, that IP is not correct. It is not the IP of the appliance per the OS, nor is it the IP of the appliance according to the setup process. I just re-ran the setup process to confirm. See attached screenshots. But I still get the wrong IP in the config file.

 

I wonder if the appliance is listening on the wrong address, and hence not receiving the broadcasts?

 

Moving the devices around is not really a practical solution at this point. 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2022-08-12 12:27 PM

In response to scottmlew_apc
0 Likes
5
2546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-12 12:27 PM

@scottmlew_apc 

 

Strange that the IP was incorrect for both PCNS and vCenter. I wonder if there is a DNS issue happening.

 

After reviewing tyour pcnsconfig.ini again I also noticed the localHostAddress =  blank

 

Since you re-ran the setup wizard stop the PowerChute service and then restart it. PCNS will recheck the accuracy of the VM IP, reconnect with vCenter, and attempt to register with the NMC since you have left the default of enrolWithNMC - true. 

 

 

To stop the service enter the command systemctl stop PowerChute (using capital P and C) 

To restart enter systemctl start PowerChute

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

scottmlew_apc
Ensign scottmlew_apc
Ensign

Posted: β€Ž2022-08-12 04:18 PM

In response to BillP
0 Likes
4
2541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-12 04:18 PM

@BillP 

 

Thank you for your continued engagement on this.

 

The vCenter IP is correct. It should be at 10.0.60.200, whereas the NMC and PCNS are both on 10.0.40.x, 150 and 10 respectively. I entered everything by IP address and just confirmed the only one of these 3 items with a DNS entry is vCenter, so even if PCNS is trying to reverse DNS itself for some reason it shouldn't come up with a bad IP address.

 

I tried restarting the service, and after that I can't connect to it at all, although the service is running. lsof shows nothing listening on any ports.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

scottmlew_apc
Ensign scottmlew_apc
Ensign

Posted: β€Ž2022-08-12 05:15 PM

In response to scottmlew_apc
0 Likes
3
2540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-12 05:15 PM

@BillP I modified the file to fix the pcns_host and also to add localHostAddress under [Networking]. When I do that and restart the service, I get a login screen, but it never advances past that screen after I enter credentials. I eventually get a 500, and I can't connect again even though it is still listening on 6547. I do note that when I get the 500, it has redirected me to /cfgwizard. I wonder if there are other things I need to fix in the file? I tried changing enrolWithNMC to false but same result.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2022-08-16 01:05 PM

In response to scottmlew_apc
0 Likes
2
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-16 01:05 PM

@scottmlew_apc 

 

A 500 error indicates corruption. It could be a corrupted pcnsconf.ini, the M11.cfg file, the Keystore, or possibly one of the java scripts. I recommend you watch the video PCNS442-vCenter7x.mp4 attached to https://www.se.com/ww/en/faqs/FA296461/ and then redeploy the PCNS VM.

 

If you are deploying a static IP address, use a different one, and use another hostname. I recommended this to prevent any DNS issues.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

scottmlew_apc
Ensign scottmlew_apc
Ensign

Posted: β€Ž2022-08-16 01:11 PM

In response to BillP
0 Likes
1
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-08-16 01:11 PM

@BillP I will watch the video and try redeploying as soon as I can, but I've already redeployed a few times. I can't see how changing the IP address and hostname would be of relevance since there are no DNS entries for PCNS, but I will try that nonetheless.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

scottmlew_apc
Ensign scottmlew_apc
Ensign

Posted: β€Ž2022-10-02 10:57 AM

In response to scottmlew_apc
0 Likes
0
2284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-10-02 10:57 AM

@BillP I was finally able to get the appliance registered. I changed the name and IP and that seems to have fixed the issue -- which honestly makes no sense (IP was on the same subnet, and there were never any DNS entries) but I will take the win πŸ™‚

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore