AP9631 not accessible via Web Browser

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 not accessible via Web Browser
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
2
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

AP9631 not accessible via Web Browser

Receiving the following when trying to hit the NMC via a web browser:

+++++++++++++++
Error: The application was not able to load.
You are attempting to access an APC device.

There was a problem loading the application. Please login to the device via telnet for more details.
+++++++++++++++


I have tried downgrading the BIN files to 5.1.3 and then upgrading back to 5.1.5. Tried manual FTP of just the Application Module BIN file. I also tried a ResetToDef but keeping the IP information. The card is installed in a Smart-UPS RT 6000 XL

I just can't seem to get the web page to load correctly.

____________________


American Power Conversion Network Management Card AOS v5.1.5
(c) Copyright 2010 All Rights Reserved Smart-UPS & Matrix-UPS APP v5.1.5
-------------------------------------------------------------------------------
Name : Unknown Date : 08/04/2011
Contact : Unknown Time : 20:23:33
Location : Unknown User : Administrator
Up Time : 0 Days 0 Hours 11 Minutes Stat : P+ N4+ N6+ A!


Type ? for command listing
Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)

apc>
apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP9631
Serial Number: ZA1032030050
Hardware Revision: 05
Manufacture Date: 08/07/2010
MAC Address: 00 C0 B7 52 4C 85
Management Uptime: 0 Days 0 Hours 2 Minutes

Application Module
---------------
Name: sumx
Version: v5.1.5
Date: Feb 25 2011
Time: 09:12:15

APC OS(AOS)
---------------
Name: aos
Version: v5.1.5
Date: Oct 7 2010
Time: 13:38:43

APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57

apc>

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
0
1572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

As far as the Manual FTP, I did do all files, but since then I did downgrade to 5.1.3 and back to 5.1.5 again using the EXE.

It is working now though but I am not sure as to what fixed it. I tried formatting the NMC right after I posted my original message and then tried upgrading via USB (per your linked instructions) but the status light on the USB kept blinking for close to an hour. I tried resetting the NMC and noticied the reset button seemed to have been stuck down. After fixing that, the NMS came back online with no IP address. I re-entered the IP information and Viola!

None the less, it's working and it's now added to our InfraStruxure Central so all is good.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
0
1572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

you can't do a manual FTP of just the application. you have to do both AOS and app.

i'd recommend redownloading the .exe file for the firmware just incase theres an issue with it then doing manual FTP of the bootmon file, then AOS, then sumx file and see what you get. ensure you follow the manual FTP instructions for AP9631 listed here-> http://nam-en.apc.com/app/answers/detail/a_id/768

since its an AP9631, USB might also be an option...thats in that link i provided too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:05 AM . Last Modified: ‎2024-03-06 03:05 AM

As far as the Manual FTP, I did do all files, but since then I did downgrade to 5.1.3 and back to 5.1.5 again using the EXE.

It is working now though but I am not sure as to what fixed it. I tried formatting the NMC right after I posted my original message and then tried upgrading via USB (per your linked instructions) but the status light on the USB kept blinking for close to an hour. I tried resetting the NMC and noticied the reset button seemed to have been stuck down. After fixing that, the NMS came back online with no IP address. I re-entered the IP information and Viola!

None the less, it's working and it's now added to our InfraStruxure Central so all is good.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore