Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

AP9631 keeps rebooting after a firmware upgrade.

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 keeps rebooting after a firmware upgrade.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:46 AM

0 Likes
8
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:46 AM

AP9631 keeps rebooting after a firmware upgrade.

This question was originally posted by Aleksey on APC forums on 6/5/2014


Hi,

I have a nework management card AP9631 on MGE Galaxy 3500 which reboots every 7-8 minutes after a firmware upgrade to UPS NMC v6.1.1.

Network settings (default gateway) is valid.

What's wrong?

Attachments
debug.txt.zip
dump.txt.zip
event.txt.zip
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:47 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:47 AM

This reply was originally posted by Aleksey on APC forums on 6/5/2014


Hi,

I have a nework management card AP9631 on MGE Galaxy 3500 which reboots every 7-8 minutes after a firmware upgrade to UPS NMC v6.1.1.

Network settings (default gateway) is valid.

What's wrong?

See Answer In Context

Reply
Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:46 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:46 AM

This reply was originally posted by Aleksey on APC forums on 6/6/2014


Hi,

We upgraded from version 5.1.7 to v6.1.1.

Here are logs without network cable before format (i removed cable in 9:20 and did the pinhole reset)...


Attachments
debug_wonetwork.txt.zip
dump_wonetwork.txt.zip
config_wonetwork.ini.zip
event_wonetwork.txt.zip
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:46 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:46 AM

This reply was originally posted by Aleksey on APC forums on 6/6/2014


...and with cable after format.

P.S. hmmmmm.... I've update files in .txt format and don't know, why they are posted in .zip.

Attachments
event_aformat.txt.zip
config_aformat.ini.zip
dump_aformat.txt.zip
debug_aformat.txt.zip
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:46 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:46 AM

This reply was originally posted by Angela on APC forums on 6/6/2014


Hmm, interesting. And thank you for all of the log files again.

And I think the forum automatically compresses any files and puts them in .zip so its not you smile

So, yes, I see that you formatted, you did not do any configurations (which is what we want) and it still does it! cry We could also try to power cycle the NMC but I don't think it will fix it.

I have a few ideas and steps assuming no change after you power cycle (or just pull out the card for 10 seconds and put it back in the UPS).

  1. Downgrade to 5.1.7 for 'kicks' and see if it behaves normally. I can provide the files if required. After you do downgrade, you should do another format to ensure integrity of the system. If it does work, let me know (depending on why you upgraded in the first place) if staying at 5.1.7 until our next release comes out is feasible.
  2. Try the card in a different UPS, if you have one available.
  3. I discuss with you offline the potential of trying a beta firmware release, which the final version is tentatively scheduled towards the end of July (but could change) and see what happens. In order to do this though, some paperwork is required..
  4. If none of this works and we don't get anywhere and it doesn't appear UPS or firmware related, the card may need to be replaced.

Thoughts?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:47 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:47 AM

This reply was originally posted by Aleksey on APC forums on 6/9/2014


Hmm... cunningforum.


1. AOS Downgrade not allowed: 611-->517

2. In Smart-UPS 700 card is notreloaded.


Thoughts?

Attachments
result.txt.zip
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:47 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:47 AM

This reply was originally posted by Angela on APC forums on 6/9/2014


Sorry, you'll need to the downgrade manually via FTP, SCP, or XMODEM. The wizard blocks a downgrade as you can see (but we are changing that in the future).

Upgrade (and downgrade) instructions for those methods are here -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US

Can I clarify what you mean about "card is not reloaded?" Do you mean the rebooting does not occur and the card acts normally?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:47 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:47 AM

This reply was originally posted by Aleksey on APC forums on 6/10/2014


In Smart-UPS 700 the rebooting does not occur and the card acts normally.

After downgrade firmware to v5.1.7 the rebooting does not occur.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:47 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:47 AM

This reply was originally posted by Angela on APC forums on 6/10/2014


Hmm, OK. How do you want to proceed? I don't know if you have another NMC to try @ 6.1.1 in the G3500 but if I had my way, that is what I would do next to see if it always points to this UPS or the NMC.

Can you stay on 5.1.7 until the next release (tentatively in a few months) or do you want to pursue other options involving beta software and the paper work (beta test sheet, etc) that will come along with that? We can at least see if the newer firmware revision behaves any differently in this UPS. I am not sure if you were upgrading to take advantage of a particular feature or just to stay up to date.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:47 AM

0 Likes
0
419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 05:47 AM

This reply was originally posted by Aleksey on APC forums on 6/5/2014


Hi,

I have a nework management card AP9631 on MGE Galaxy 3500 which reboots every 7-8 minutes after a firmware upgrade to UPS NMC v6.1.1.

Network settings (default gateway) is valid.

What's wrong?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc