AP9631 - No shutdown menu

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 - No shutdown menu
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
7
2298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

AP9631 - No shutdown menu

I am trying to configure the network management card. It has been in operation for 2 months and since it is a refurb when I received it I updated it to v6.9.6 and at that time configured a APC appliance on a VMware and do not recall of any problems.

Now I just added a new server and a Synology and neither the SNMP or any of the APC appliance or even Network shutdown installed on a server can connect to the card. 

During to process I wanted to change the authentication phrase but the menu Shutdown under Configuration seems to have disappeared (attached picture). 

Anyone had that happened to them ? Maybe I missed something big time....   

thanks you all. 

 

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:18 AM

On 3/1/2021 3:02 PM, Bill said:

This is the firmware needed for a Smart-UPS 

e2pKlVPrEjEUhb%2FlVW6Uiw%3D%3D.pnge2pKlVPrEjEUhb%2FlVW6Uiw%3D%3D.png

I'm really glad I found this post.

I have been an APC user and installer for close to 30 years now.

I spent over an hour today looking for the firmware you posted a link to here. No matter how I searched on the "downloads" page, it was impossible to locate. It kept sending me to firmware for the Symmetra devices - regardless the fact that I had never specified that product in the search terms - which based on past experience would break a lot of things if you attempted to install that on a card being used in a SmartUPS. (SMT1500 in this particular case)

I had similar issues with the UPS firmware.

Is it my imagination or is the Schneider version of the APC website a giant mess now?

 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

Hi,

You are not logging into the card with administrators privileges and therefore cannot edit/see the settings. Log out and log in as an administrator.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

Hi Bill,

Thanks for taking the time to write me on this. Yes I am logged has admin with the apc user. I also did a complete reset of the thing and nothing. Can't get anything to connect or authenticate to it and the Shutdown menu is nowhere to be found. Very strange never seen that before.

Since I do not have the Shutdown menu I can't set or change the authentication phrase so I also tried the SNMP from my NAS and a big nothing on any settings.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

Hi,

 

Would you attach a screenshots of the About - UPS and About - Network pages?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

Sure here it is.

By the way the unit was sold as refurbish a couple of months back and the seller just mentioned he would send me a replacement. Still. The behaviour is weird. I'll try to report my findings. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

Hi,

What is the model of the UPS. The screenshot attached shows the model of the NMC and the NMC firmware. The firmware installed is for a Symmetra UPS. If your UPS is a Smart-UPS then you need to install the correct firmware. 

This is the firmware needed for a Smart-UPS 

WN1cKPoqytW0dVQ5OJizGQ%3D%3D.pngWN1cKPoqytW0dVQ5OJizGQ%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:17 AM . Last Modified: ‎2024-03-08 01:18 AM

Hi Bill, 

This would make sense I didn't know there were 2 different firmware for the card. The USP is a SMT1500RM2U.

It is very strange because I did configure an APC appliance on it when I got it originally. 

I suppose that is the issue. What is the difference for symmetra it looks the same just thought the Shutdown menu was not there. 

BTW thanks for the info I really appreciate. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:18 AM

0 Likes
0
2300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:18 AM . Last Modified: ‎2024-03-08 01:18 AM

On 3/1/2021 3:02 PM, Bill said:

This is the firmware needed for a Smart-UPS 

e2pKlVPrEjEUhb%2FlVW6Uiw%3D%3D.pnge2pKlVPrEjEUhb%2FlVW6Uiw%3D%3D.png

I'm really glad I found this post.

I have been an APC user and installer for close to 30 years now.

I spent over an hour today looking for the firmware you posted a link to here. No matter how I searched on the "downloads" page, it was impossible to locate. It kept sending me to firmware for the Symmetra devices - regardless the fact that I had never specified that product in the search terms - which based on past experience would break a lot of things if you attempted to install that on a card being used in a SmartUPS. (SMT1500 in this particular case)

I had similar issues with the UPS firmware.

Is it my imagination or is the Schneider version of the APC website a giant mess now?

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore