AP9631 Firmware downgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 Firmware downgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
anton_au_apc
Crewman anton_au_apc
Crewman

Posted: ‎2021-06-28 07:18 AM . Last Modified: ‎2024-03-18 12:33 AM

0 Likes
7
6240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:18 AM . Last Modified: ‎2024-03-18 12:33 AM

AP9631 Firmware downgrade

I have not been able to find anything on google or on this site. i have a simple issue.

I've upgraded firmware on my NM2 card to 6.5 but it does not support UPS firmware version. So now UPS is not recognised. I cannot find a repository of older firmware versions for this card. Can i get a link please.

UPS is 3000RMI2U Ups upgraded to latest available fw

Just need a link to various FW versions, there is plenty of doco on how to do it.

Thank you

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
anton_au_apc
Crewman anton_au_apc
Crewman

Posted: ‎2021-07-04 03:51 AM

In response to BillP
0 Likes
0
6234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-04 03:51 AM

Hi,

 

Not sure why this is being responded to now, I've all of a sudden got a email there is a reply. I believe the discussion is from 3 years ago. I no longer have an issue and while I've resolved the above, I do not remember how. Would have been just research and googleing.

 

SKU: SMT3000RMI2U

My UPS FW is UPS 09.4 (ID18)

My NW FW is Version v6.5.6

 

If there is a newer version on and FTP somewhere, share the link so that people can use them.

 

Other than that, we can close this thread out as I don't have any problems with the unit at the moment. I try to keep FW/APP version up to date for security and long term functionality compatibility.

 

Cheers,

Anton

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-28 07:18 AM . Last Modified: ‎2024-03-18 12:33 AM

0 Likes
0
6238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:18 AM . Last Modified: ‎2024-03-18 12:33 AM

I don't think they remove support for old UPSes from the firmware.

Did you wait for 15 minutes after the firmware upgrade to give the card time to reinitialise and reconnect to the UPS?  It will show up as if it can't find the UPS if you try to connect to the card too quickly after the firmware upgrade completes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:18 AM . Last Modified: ‎2024-03-18 12:33 AM

0 Likes
0
6238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:18 AM . Last Modified: ‎2024-03-18 12:33 AM

3000RMI2U sounds specifically like a Smart-UPS product type. You don't necessarily need to downgrade but rather re-apply v6.5.0 with the correct application bundled. We can confirm that if you share which specific filename you downloaded and applied. Or, if you log into the web, see what it says at the top. It should say "Smart-UPS/Matrix Application" and currently you may see Symmetra Application or something. You can also verify what is showing under About->Network which should say your application name is 'sumx' and now it probably says something different.

BKNgUiEwTfDgoxL8nsizmg%3D%3D.pngBKNgUiEwTfDgoxL8nsizmg%3D%3D.png

I suggest you try to apply this firmware and re-check to make sure your UPS is discovered.

http://www.apc.com/shop/us/en/products/UPS-NMC-v6-5-0-for-Smart-UPS-with-AP9630-31-35-Critical-Revie... 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

0 Likes
0
6238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

I forgot to say if it already says Smart-UPS/Matrix application, then we should try a few more things, like verifying there is nothing connected to the UPS serial port which can cause this problem on some models after an NMC reboots, which happens during firmware upgrade. It is likely not a firmware specific thing and we can get 6.5.0 to work properly. Most common issue is accidentally applying the wrong application file for the particular device type.

Reply

Link copied. Please paste this link to share this article on your social media post.

anton_au_apc
Crewman anton_au_apc
Crewman

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

0 Likes
0
6238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

Thank you will try above and report back.

Reply

Link copied. Please paste this link to share this article on your social media post.

anton_au_apc
Crewman anton_au_apc
Crewman

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

0 Likes
0
6238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

Hi Angela,

Appreciate your advice, I have downloaded the firmware you suggested and tried re-flashing. It is now working fine and UPS is being detected (SMT3000RM2U)

I suspect you are correct where Symmetra version was applied. It was not clear to me on the site the difference in the downloads for the interface model.

For future reference, is it possible to still provide a link (If one is available) to older firmware versions? Or is it something that needs to be specifically requested? I've found many articles (KB) and discussions on this site around downgrading frimware, but no location for the actual firmware files.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

0 Likes
1
6238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:19 AM . Last Modified: ‎2024-03-18 12:33 AM

Hi Anton,

Yes, we can provide the older firmwares if needed for a certain reason or for troubleshooting. They are also still available on our FTP site which is where we can link them from. But if downgrading without specific assistance or guidance from us, I would observe caution as downgrading isn't officially supported, especially between major firmware versions, like v6.X.X and v5.X.X revs of firmware. Between minor versions is generally OK but there is just that disclaimer.

Reply

Link copied. Please paste this link to share this article on your social media post.

anton_au_apc
Crewman anton_au_apc
Crewman

Posted: ‎2021-07-04 03:51 AM

In response to BillP
0 Likes
0
6235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-04 03:51 AM

Hi,

 

Not sure why this is being responded to now, I've all of a sudden got a email there is a reply. I believe the discussion is from 3 years ago. I no longer have an issue and while I've resolved the above, I do not remember how. Would have been just research and googleing.

 

SKU: SMT3000RMI2U

My UPS FW is UPS 09.4 (ID18)

My NW FW is Version v6.5.6

 

If there is a newer version on and FTP somewhere, share the link so that people can use them.

 

Other than that, we can close this thread out as I don't have any problems with the unit at the moment. I try to keep FW/APP version up to date for security and long term functionality compatibility.

 

Cheers,

Anton

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore