Symmetra RM dropping load coming out of bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM dropping load coming out of bypass
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

0 Likes
5
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

Symmetra RM dropping load coming out of bypass

I just can't seem to solve this one. Symmetra RM kicked on to battery backup during a recent power outage. All systems were shut down gracefully, and the UPS was powered off to silence alarms, and as we knew the outage would be an extended one.

 

Power was restored the following day, but the Symmetra refused to power up until I put it into Bypass using the breaker on the rear. That brought the UPS up, but obviously in Bypass mode, with the amber light on the LED panel indicating such. All my attempts to power up attached equipment fail when I take the unit out of Bypass mode with the breaker on the rear. Attached equipment works fine while in Bypass, but I lose all power to attached equipment as soon as a flip the breaker out of Bypass (although the LED panel remains fully functional).

 

Using the LED panel to bring the system out of Bypass when it's in this limbo state is not successful.

 

Power modules show as 'Off and OK' when in breaker-induced Bypass, and 'On and OK' when in the limbo state (when Bypass breaker is in the 'Out of Bypass' position, i.e. when there is no output)

 

LED shows Charge 99%, Load 35%, Voltage 239V in 240V out (60 Hz), runtime 22 minutes.

So, I'm stuck in a state where a 1 second power interruption (frequent in my area) brings my entire rack down.

 

Any thoughts or ideas?

 

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • bypass
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-03 06:21 PM

0 Likes
0
1643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-03 06:21 PM

Old topic, but thought I'd share the solution anyway.

 

Despite the fact there were no meaningful messages, it was the Main Intelligence Module. I rolled the dice and picked one up and the problem was solved. Very odd the the redundant Intelligence Module didn't take over, as it also tested as OK. I went ahead and replace that too.

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

Hi Jeremy,

I would strongly advise calling into Single Phase Symmetra Technical Support for an issue like this.  Aside from the "Load On" and "Bypass" LED indicators, is there a fault indicator lit?  What are the LED light patterns on the intelligence modules?  What are the states of your batteries aside from having a charge of 99% (this is a big reason a unit may not transfer to online operation - specifically battery bus voltage, age, temperature)?  Have any of the power modules or intelligence modules been replaced?  This is a complex issue that I once again advise calling into APC about to receive full support and come to an issue resolution.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

Thanks for the response, sorry for my slow reply.

No fault indicator lights on.

Battery modules are approximately 18 months old. Reported battery voltages are 120.0V Nominal and 138.1V Actual. Showing 2 Batteries, 0 Bad.

Showing 3 Power Modules, 0 Bad.

Intelligence Module showing all green.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:16 PM . Last Modified: ‎2024-03-19 12:13 AM

Hi Jeremy,

Have you increased your load on the RM at all (ie. attached more equipment to the unit that could be overloading the unit when it tries to run online and commands the unit to drop the load rather than return to bypass)?

What is the setting you have on the RM under the menus "Setup -> Bypass"?  There are two options, "go to bypass" and "drop load". 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:17 PM . Last Modified: ‎2024-03-19 12:13 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:17 PM . Last Modified: ‎2024-03-19 12:13 AM

No change in load, sitting at 33%.

Setting is 'Go to bypass'.

I did have a lengthy call with support, and they are at a loss as to why it's not working. Someone senior is supposed to be getting back to me in the coming days.

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-03 06:21 PM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-03 06:21 PM

Old topic, but thought I'd share the solution anyway.

 

Despite the fact there were no meaningful messages, it was the Main Intelligence Module. I rolled the dice and picked one up and the problem was solved. Very odd the the redundant Intelligence Module didn't take over, as it also tested as OK. I went ahead and replace that too.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of