AP9630 stack 36 overrun 1min restart loop

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9630 stack 36 overrun 1min restart loop
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Jerome_bana_apc
Crewman Jerome_bana_apc
Crewman

Posted: ‎2021-07-29 11:01 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
4
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:01 PM . Last Modified: ‎2024-02-14 02:22 AM

AP9630 stack 36 overrun 1min restart loop

Hi

We got 4 smart ups 5000 with network management card, 3 got ap9617 and work fine but for some reason the one with AP9630 seems stuck in a loop of stack overrun and warmstart.
Attached to this post is the 3 files suggested for support, config.ini, event.txt and data.txt.

the firmwares used are :
Network Management Card AOS v5.0.1

Smart-UPS

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jerome_bana_apc
Crewman Jerome_bana_apc
Crewman

Posted: ‎2021-07-29 11:02 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:02 PM . Last Modified: ‎2024-02-14 02:22 AM

Hi

We got 4 smart ups 5000 with network management card, 3 got ap9617 and work fine but for some reason the one with AP9630 seems stuck in a loop of stack overrun and warmstart.
Attached to this post is the 3 files suggested for support, config.ini, event.txt and data.txt.

the firmwares used are :
Network Management Card AOS v5.0.1

Smart-UPS

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Jerome_bana_apc
Crewman Jerome_bana_apc
Crewman

Posted: ‎2021-07-29 11:01 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:01 PM . Last Modified: ‎2024-02-14 02:22 AM

seems upgrading firmware to 5.1.1 fixed the problem, 5 min no warmstart again.

edit : I was wrong :
19.05.2010 13:14:04 UPS: Restored the local network management interface-to-UPS communication.
19.05.2010 13:13:50 System: Network service started. System IP is 10.0.0.28 from manually configured settings.
19.05.2010 13:13:41 System: Warmstart.

Message was edited by: Jerome_bana

Reply

Link copied. Please paste this link to share this article on your social media post.

Jerome_bana_apc
Crewman Jerome_bana_apc
Crewman

Posted: ‎2021-07-29 11:01 PM . Last Modified: ‎2024-02-14 02:31 AM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:01 PM . Last Modified: ‎2024-02-14 02:31 AM

the update changed the stack overrun thing.

now it does still warmstart but only every 12 min ish

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:02 PM . Last Modified: ‎2024-01-29 11:38 PM

0 Likes
0
2028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:02 PM . Last Modified: ‎2024-01-29 11:38 PM

if you FTP to the card and navigate to the /dbg directory, is there a text file in there that you can download? or paste the contents of the file?

also, i attached firmware 5.1.3 for smart ups to this post, it is the latest version.

please see if you can upgrade to that for us. you can check the /dbg directory first for that file though.

Reply

Link copied. Please paste this link to share this article on your social media post.

Jerome_bana_apc
Crewman Jerome_bana_apc
Crewman

Posted: ‎2021-07-29 11:02 PM . Last Modified: ‎2024-02-14 02:22 AM

0 Likes
0
2029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:02 PM . Last Modified: ‎2024-02-14 02:22 AM

Hi

We got 4 smart ups 5000 with network management card, 3 got ap9617 and work fine but for some reason the one with AP9630 seems stuck in a loop of stack overrun and warmstart.
Attached to this post is the 3 files suggested for support, config.ini, event.txt and data.txt.

the firmwares used are :
Network Management Card AOS v5.0.1

Smart-UPS

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore