Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

ACRD602 Problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRD602 Problem
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:03 PM

0 Likes
14
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:03 PM

ACRD602 Problem

This question was originally posted by Rami on APC forums on 1/9/2019


Hello,

I found uncommon problem with my 3 units ACRD602P working as HACS.

The Units stop cooling, and kept in ON and Backup mode, and shown that the Group cooling demand as 0kW, since the temperature in the Datacenter more than the usual and set point which it is 22C.

LG3QaNARW%2BsHGC4V5Gnv5w%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

I'm attaching the events log for the three units CB1, CB2, and CB3, and data log. in addition to report for the input voltage and Group maximum temperature report

please find the attached

you can go to the events; you will found that the problem occurs three times: at

08/01/2019 2:17PM up to 3:33PM

08/01/2019 9:37PM up to 10:45PM

09/01/2019 8:51AM up to 10:01PM

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:03 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:03 PM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 1/10/2019


Hello Rami. I recommend you call into your local tech support on this issue when you have access to all three of these units either over the web or from the front screen. This issue can be caused by a lot of different factors and may take some adjustments to the setup of the units which is better done over the phone.

A couple of things to look at are: When in HACS mode the unit does not look at the Rack inlet sensor for the cooling demand. the unit is looking at the difference between the return air temperature and the supply air setpoint. It is waiting for the proper delta between these values (determined by your fan speed preference) to know when to turn on. Make sure there are no gaps between the equipment in the racks that will allow the server exhaust air to travel to the front of the rack without going through the cooling unit. If there are gaps this will heat up the rack inlet sensor and cause it to read high. We want all the server exhaust air to be returned to the cooling unit for the heat to be removed.

I am only seeing a 15 kw load in the logs for the group. This is about the minimum amount of heat load to run one of these units. Ideally we would like some more heat load to keep the units running all the time. If you are still building out the room, when more servers are added, this will improve the performance of the cooling units. In the mean time, please call into your local tech support and they can help you change some settings to keep the units running better in the current environment. 

Thank you

See Answer In Context

Reply
Share
Replies 14
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:03 PM

0 Likes
0
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:03 PM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 1/10/2019


Hello Rami. I recommend you call into your local tech support on this issue when you have access to all three of these units either over the web or from the front screen. This issue can be caused by a lot of different factors and may take some adjustments to the setup of the units which is better done over the phone.

A couple of things to look at are: When in HACS mode the unit does not look at the Rack inlet sensor for the cooling demand. the unit is looking at the difference between the return air temperature and the supply air setpoint. It is waiting for the proper delta between these values (determined by your fan speed preference) to know when to turn on. Make sure there are no gaps between the equipment in the racks that will allow the server exhaust air to travel to the front of the rack without going through the cooling unit. If there are gaps this will heat up the rack inlet sensor and cause it to read high. We want all the server exhaust air to be returned to the cooling unit for the heat to be removed.

I am only seeing a 15 kw load in the logs for the group. This is about the minimum amount of heat load to run one of these units. Ideally we would like some more heat load to keep the units running all the time. If you are still building out the room, when more servers are added, this will improve the performance of the cooling units. In the mean time, please call into your local tech support and they can help you change some settings to keep the units running better in the current environment. 

Thank you

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:03 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:03 PM

This reply was originally posted by Rami on APC forums on 1/12/2019


Dear Sir/Madam,

I can get all the units configuration, and send them to you if you are interested.

I'm contacting Schneider in Israel, but due to political issues, they can't access the Palestinian Territories. then we will try to solve it remotely.

I made two units to run, because the room is big, please check the attached.

you saw also that the cooling loads not exceeding 15kW, every one min the 2 units working for 2 min.

Also I need your recommendation to connect at least one unit at UPS, because the electricity fails in the winter 2 times a day, so all the cooling units shutdown, what do you recommend? 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:03 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:03 PM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 1/14/2019


Hello Rami.

We usually do not recommend putting DX units on UPS's. This is because the start up demands of the compressor will overload most UPS's unless the UPS is very over sized. This usually makes it impractical to buy a UPS that big. You can work wil the sales teams to find out a UPS that would work with the RD602 and see if it is practical for your situation.

For the running of theses units, as mentioned before the load in the room is low for these units. The ideal fix would be to add more load to the room. This will keep the units on instead of cycling on and off. A few things you can do is to make sure there are no gaps in the server racks to help get the hot air back to the cooling units. Place blanking panels if there are any gaps in the racks. We can also try putting the units to Inrow mode. This will run off the rack inlet temps and may kick the units on quicker to keep those rack inlet temps from spiking.

Thank you

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:03 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:03 PM

This reply was originally posted by Rami on APC forums on 1/17/2019


Dear Sir,

Thank you very much

I Have 2  100kW UPSs with 15% load

I can make two backup units of DX units, and make one working

what is your opinion? 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by Rami on APC forums on 1/17/2019


Today the problem occurred once again, please check the attachments to have more information about the problem, also I get a screen shot for configuration and photos for the expansion tanks 

Configuration files attached in RAR file 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 1/18/2019


Hello Rami.

From the data logs it looks like there are a couple of the rack inlet sensors that are picking up heat from outside sources. Check the placement of the sensors and make sure they are not picking up heat from servers. Also make sure that there are blanking panels installed in the server racks to make sure there is no exhaust air returning through gaps. For the configuration of the room, is there a HACS containment system installed or is it open to the room?

For the question on using a UPS to power these units, I will have to direct you to the sales team to discuss. They will need to make sure your UPS can take the start up amperage of the cooling unit without getting overloaded on a circuit.

Thank you

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by Rami on APC forums on 1/19/2019


Hello,

If you checked the logs, you will see that the problem occurred in the period of 10:45 - 11:20AM, the Data center manager force on the units.

I have checked the three Units' logs, and found:

CB1: 

Supply Air Temp: 23.5C

Racks Inlet: 22-24C

CB2: 

Supply Air Temp: 23.5-27C

Racks Inlet: 22-29C

CB3: 

Supply Air Temp: 23.5-27C

Racks Inlet: 21-24C

Then the temperature is real one, not occurred because of hot air coming from servers.

if you have a look on Group demand  (GrpCoolDmd.kW) was ZERO

I saw that the superheat in some logs is OutOfRange

There are blanking panels, and the hot aisle is totally isolated.

for HACS, yes we are using Hot aisle containment by APC, and Blanking panels.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 1/22/2019


Hello Rami.

From the logs the units are turning off as they are satisfying the cooling in the room. It is during this time when they are off that we are seeing the rack inlet temps rise on a few racks. In HACS mode the units do not look at the rack inlet sensors to determine when cooling is needed. The units are looking at the return air temp and the supply air setpoint to try and keep a delta between these two values. What is the fan speed preference set to on the units (this is found under group tab and setpoints). Try raising the fan speed preference (ie if it is set to medium, set it to medium-high). This will lower the delta that the unit is looking for between the return air and the supply air setpoint and will kick on the units quicker. The fans will run at a higher speed as well.

Thank you

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by Rami on APC forums on 1/24/2019


Hello,

the Cooling set point is 22C and the Supply air is 18C, I don't that the units stop working because of Delta Temp, the supply air reached 27C in some units.

The Fan speed set to be Automatic and High 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 1/28/2019


I would suggest to remove the unit on the side by itself from the group and put that unit to Inrow. This will have that unit look at the rack inlet temps to determine when to turn on. Leave the other two units in a group of 2 with one backup unit in HACS. This will try to smooth out the hot spots so the temps do not rise as much when the units are off after they satisfied their cooling.

Thank you

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by Rami on APC forums on 2/5/2019


Hello,

Since there is no load, then I made one unit working and two backup, I asked the customer to increase the loads, but he can't do that. this load is the maximum.

I change some configuration as:
Supply Air: 18C

Re-Heat: 17C

Cooling Set Point: 22C

What are you recommend to increase the loads?

The unit giving: Excessive Compressor Cycling Condition.  warning

many thanks

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by L2SupportServices-Cooling on APC forums on 2/6/2019


Hello. The main way to increase the load is to add in more equipment but it sounds like they are maxed out on their servers. Check to make sure there is no building a/c vent coming into the room. If there is see if you can close it and allow the inrow units to cool the room.

Thank you

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by Rami on APC forums on 2/7/2019


Hello,

It is full isolated 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 11:04 PM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-29 11:04 PM

This reply was originally posted by Rami on APC forums on 2/19/2019


Dears,

the problem solved

I will increase the loads

many thanks

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc