Hi!
Since APC is not willing to open microlink protocol we were forced to buy a NMC 2 AP9630.
Now I try to configure it and I'm not able to set
PowerNet-MIB::upsBasicIdentName.0
System Name is set in webinterface, but doesn't show up as BasicIdent. Even setting it with snmpset succeeds, but the value doesn't show up using snmpget afterwards. It's empty all the time.
Firmware is v5.0.1. UPS is a RT3000.
Any suggestions?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:39 AM . Last Modified: 2024-03-07 02:43 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:39 AM . Last Modified: 2024-03-07 02:43 AM
no, I'm talking about
.1.3.6.1.4.1.318.1.1.1.1.1.2.0 == PowerNet-MIB::upsBasicIdentName.0
which is documented as read/write value. In fact this value is empty (not set by any web interface field), and a snmpset is successful, but the value is still empty on the next read.
apcupsd reads this value as name. so i need to set that value as defined in APC PowerNet MIB documentation.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:39 AM . Last Modified: 2024-03-07 02:43 AM
>
no, I'm talking about
.1.3.6.1.4.1.318.1.1.1.1.1.2.0 == PowerNet-MIB::upsBasicIdentName.0
which is documented as read/write value. In fact this value is empty (not set by any web interface field), and a snmpset is successful, but the value is still empty on the next read.
apcupsd reads this value as name. so i need to set that value as defined in APC PowerNet MIB documentation.
>
Your UPS model doesn't support storing a name. On the NMC web interface, we're using the system name (system.sysName.0) instead. In the future, I suspect we won't respond to upsBasicIdentName if the UPS does not support it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:39 AM . Last Modified: 2024-03-07 02:43 AM
If you're talking about the Identification information in the web interface under Administration->General->Identification, the corresponding OID is system.sysName.0 (.1.3.6.1.2.1.1.5.0). Location and Contact are under the same MIB branch.
Let me know if that helps.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:39 AM . Last Modified: 2024-03-07 02:43 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:39 AM . Last Modified: 2024-03-07 02:43 AM
no, I'm talking about
.1.3.6.1.4.1.318.1.1.1.1.1.2.0 == PowerNet-MIB::upsBasicIdentName.0
which is documented as read/write value. In fact this value is empty (not set by any web interface field), and a snmpset is successful, but the value is still empty on the next read.
apcupsd reads this value as name. so i need to set that value as defined in APC PowerNet MIB documentation.