Hi all,
it seems i have a very commond problem with my NMC2 AP9630
It cant communicate with my UPS
I already tried rebooting, FW Updates, Reset
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 10:02 AM . Last Modified: ‎2024-03-15 06:06 AM
Try swapping the network cards to see if its a fault with the card or the UPS. If its the card, try upgrading the card firmware, download the upgrade file from the WEB, even if its the same version as your file might be corrupt.
By the way, unplugging the card only reboots the card. The configuration is still stored within the card.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 10:02 AM . Last Modified: ‎2024-03-15 06:06 AM
Try swapping the network cards to see if its a fault with the card or the UPS. If its the card, try upgrading the card firmware, download the upgrade file from the WEB, even if its the same version as your file might be corrupt.
By the way, unplugging the card only reboots the card. The configuration is still stored within the card.