AP9630 Firmware Upgrade Failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9630 Firmware Upgrade Failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:58 AM . Last Modified: ‎2024-03-06 12:02 AM

0 Likes
1
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:58 AM . Last Modified: ‎2024-03-06 12:02 AM

AP9630 Firmware Upgrade Failure

Hi All,

I have 2 APC Smart-UPS 3000VA RM with AP9630 management cards. I can't get either card to upgrade using the Windows tools, FTP or SCP. Each attempt fails. Here is their current >about

apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP9630
Serial Number: BA0908004529
Hardware Revision: 05
Manufacture Date: 02/17/2009
MAC Address: 00 C0 B7 D7 B1 10
Management Uptime: 0 Days 0 Hours 2 Minutes

Application Module
---------------
Name: sumx
Version: v5.0.0
Date: Nov 25 2008
Time: 14:55:35

APC OS(AOS)
---------------
Name: aos
Version: v5.0.1
Date: Nov 25 2008
Time: 12:09:34

APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.0
Date: Oct 8 2008
Time: 16:03:02

I'm trying to install 5.1.7 from the APC web site, apc_hw05_aos517_sumx517_bootmon102.exe but it just won't work.

The Windows tools gives me this...

Starting Upgrade 12/31/12: 11:13:50
-----------------
12/31/12: 11:13:50 192.168.2.141: Testing device connection
12/31/12: 11:13:50 192.168.2.141: Device connection passed
12/31/12: 11:13:51 192.168.2.141: Testing FTP Log-in
12/31/12: 11:13:54 192.168.2.141: FTP Log-in passed
12/31/12: 11:13:55 192.168.2.141: Saving data file
12/31/12: 11:15:10 192.168.2.141: Information --> Unable to verify previous version

Anyone got any ideas?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:58 AM . Last Modified: ‎2024-03-06 12:02 AM

0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:58 AM . Last Modified: ‎2024-03-06 12:02 AM

Unless you absolutely need this tonight for some reason, I'd suggest waiting for one of the APC folks here to answer.

On the AP9617/8/9 you can do manual FTP's to the unit and "put" the new AOS file to it. It should reboot and then you FTP to it and "put" the APP file to it. The only reasons I'm urging caution are: A) you can "brick" the unit doing this if you don't get everything exactly right (like sending the wrong file for the hardware) and B) I haven't tried it on an AP9630/9631 and thus don't know if you're supposed to also send the bootmon file (or in what sequence).

Again, I'd urge you to wait for an APC reply unless you have to get it done tonight and understand the risks I've outlined above.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:58 AM . Last Modified: ‎2024-03-06 12:02 AM

0 Likes
0
2074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:58 AM . Last Modified: ‎2024-03-06 12:02 AM

Unless you absolutely need this tonight for some reason, I'd suggest waiting for one of the APC folks here to answer.

On the AP9617/8/9 you can do manual FTP's to the unit and "put" the new AOS file to it. It should reboot and then you FTP to it and "put" the APP file to it. The only reasons I'm urging caution are: A) you can "brick" the unit doing this if you don't get everything exactly right (like sending the wrong file for the hardware) and B) I haven't tried it on an AP9630/9631 and thus don't know if you're supposed to also send the bootmon file (or in what sequence).

Again, I'd urge you to wait for an APC reply unless you have to get it done tonight and understand the risks I've outlined above.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore