How can i change a event severity group?
For example:
UPS: On battery power in response to an input power problem. [0x0109]
I want change this event from warning events to critical events.
Thanks for advice
.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:54 AM . Last Modified: 2024-03-05 01:54 AM
You're welcome
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:54 AM . Last Modified: 2024-03-05 01:54 AM
First you need to find out what firmware is of the AP9619, and if you are running 3.X firmware the severity level/group cannot be changed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:54 AM . Last Modified: 2024-03-05 01:54 AM
Firmware version is 3.5.5, that's means that i can't modify.
Thanks for your help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:54 AM . Last Modified: 2024-03-05 01:54 AM
You're welcome