Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

AP9619 snmp/nagios OID listing/decryption

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9619 snmp/nagios OID listing/decryption
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
unclecameron_apc
Crewman unclecameron_apc
Crewman

Posted: ‎2021-06-30 11:17 PM

0 Likes
5
544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 11:17 PM

AP9619 snmp/nagios OID listing/decryption

This was originally posted on APC forums on 2/9/2011


I am using the following MIB's with snmpget/nagios fine:
......
.1.3.6.1.4.1.318.1.1.1.2.1.1.0 Main Battery Status
.1.3.6.1.4.1.318.1.1.10.2.3.2.1.4.1 Environment Temperature in degree F
.1.3.6.1.4.1.318.1.1.1.2.2.1.0 Battery Capacity %
.1.3.6.1.4.1.318.1.1.1.2.2.2.0 Internal Temperature in degree celsius
.1.3.6.1.4.1.318.1.1.1.4.2.3.0 Output Load %
.1.3.6.1.4.1.318.1.1.1.4.2.4.0 Output Current in Ampere 3~'
.1.3.6.1.4.1.318.1.1.1.4.2.1.0 Output Voltage in Volt 3~'
.1.3.6.1.4.1.318.1.1.1.4.2.2.0 Output Frequency in Herz'
......
but can't figure out the OID I need to get battery runtime, I want to get several more data points, is there a list somewhere? I've run snmpwalk, but need help decoding the big long list it produces so I can port it to nagios check_snmp.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
unclecameron_apc
Crewman unclecameron_apc
Crewman

Posted: ‎2021-06-30 11:17 PM

0 Likes
0
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 11:17 PM

This was originally posted on APC forums on 4/1/2011


turns out the OID was correct, but check_snmp in nagios isn't convering units when used in conjunction with -w and -c (warning and critical) flags enabled for some reason, so this

check_snmp -H 1.2.3.4 -o .1.3.6.1.4.1.318.1.1.1.2.2.3.0 -l 'Runtime Remaining' -u 'Minutes'

returns

SNMP OK - Runtime Remaining Timeticks: (132000) 0:22:00.00 Minutes |

but wouldn't trigger an event if it was low, making nagios3 notification useless, but this:

check_snmp -H 1.2.3.4 -o .1.3.6.1.4.1.318.1.1.1.2.2.3.0 -w 130000 -c 100000 -l 'Runtime Remaining' -u 'Minutes'

returns the output in seconds for some reasons like

SNMP CRITICAL - Runtime Remaining *132000* Minutes | Runtime Remaining=132000

and does the same if I specify units in minutes too. I've looked into the various range formats you can specify for units, but haven't found much, even after asking on the nagios users list, I don't know what to do, this must be a common requirement: monitor apc9619 runtime in minutes with threshold triggers on a Debian Squeeze Nagios3 server, should be simple I'd think.

See Answer In Context

Reply
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:17 PM

0 Likes
0
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 11:17 PM

This reply was originally posted by Jonathan on APC forums on 2/10/2011


On the UPS that I have, I used the OID of .1.3.6.1.4.1.318.1.1.1.2.2.3.0 to get the Runtime Remaining (upsAdvBatteryRunTimeRemaining). I hope this is the one that you are looking for, by the way the UPS that I used was a regular APC Smart-UPS (SUA1500RM2U).

Reply
unclecameron_apc
Crewman unclecameron_apc
Crewman

Posted: ‎2021-06-30 11:17 PM

0 Likes
0
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 11:17 PM

This was originally posted on APC forums on 2/11/2011


thanks. Somehow I get a battery-runtime of 132000 minutes, is that a unit or config issue, or am I looking at the wrong oid?

Reply
unclecameron_apc
Crewman unclecameron_apc
Crewman

Posted: ‎2021-06-30 11:17 PM

0 Likes
0
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 11:17 PM

This was originally posted on APC forums on 2/11/2011


I guess the bigger question is how would I find out the overall schema, trying to understand how to understand the OID's on a snmp device, starting with this one.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:17 PM

0 Likes
0
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 11:17 PM

This reply was originally posted by Angela on APC forums on 2/11/2011


sometimes it will give you the runtime in seconds or a different, unexpected unit of measure. you may want to use a MIB browser or another tool that also gives you the descriptions of the OIDs to find out what unit the value returns in or to see if you have to move the decimal point, etc

Reply
unclecameron_apc
Crewman unclecameron_apc
Crewman

Posted: ‎2021-06-30 11:17 PM

0 Likes
0
544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 11:17 PM

This was originally posted on APC forums on 4/1/2011


turns out the OID was correct, but check_snmp in nagios isn't convering units when used in conjunction with -w and -c (warning and critical) flags enabled for some reason, so this

check_snmp -H 1.2.3.4 -o .1.3.6.1.4.1.318.1.1.1.2.2.3.0 -l 'Runtime Remaining' -u 'Minutes'

returns

SNMP OK - Runtime Remaining Timeticks: (132000) 0:22:00.00 Minutes |

but wouldn't trigger an event if it was low, making nagios3 notification useless, but this:

check_snmp -H 1.2.3.4 -o .1.3.6.1.4.1.318.1.1.1.2.2.3.0 -w 130000 -c 100000 -l 'Runtime Remaining' -u 'Minutes'

returns the output in seconds for some reasons like

SNMP CRITICAL - Runtime Remaining *132000* Minutes | Runtime Remaining=132000

and does the same if I specify units in minutes too. I've looked into the various range formats you can specify for units, but haven't found much, even after asking on the nagios users list, I don't know what to do, this must be a common requirement: monitor apc9619 runtime in minutes with threshold triggers on a Debian Squeeze Nagios3 server, should be simple I'd think.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc