AP9619 not accessable after firmware upgrade to 3.7.3
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0106:25 AM. Last Modified: 2024-03-0411:36 PM
Hi. When you telnet in, what do you see on the top right of the screen? There should be an AOS and APP with their version numbers listed. If you just see an AOS, then there was likely a blip with the firmware upgrade.
Either way, most of the time, you just need to try the upgrade again and run it manually, like by FTP. Instructions are here below and you need to push AOS 3.7.3, let the NMC reboot, then push your application file and let it reboot.
if that doesn't work, FTP in and let me know what AOS number is written when you log in - it will say something like AOS 3.7.3 FTP server ready upon logging in.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0106:25 AM. Last Modified: 2024-03-0411:36 PM
Hi. When you telnet in, what do you see on the top right of the screen? There should be an AOS and APP with their version numbers listed. If you just see an AOS, then there was likely a blip with the firmware upgrade.
Either way, most of the time, you just need to try the upgrade again and run it manually, like by FTP. Instructions are here below and you need to push AOS 3.7.3, let the NMC reboot, then push your application file and let it reboot.
if that doesn't work, FTP in and let me know what AOS number is written when you log in - it will say something like AOS 3.7.3 FTP server ready upon logging in.