AP9617 hangs SmartUPS-1400

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9617 hangs SmartUPS-1400
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

0 Likes
12
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

AP9617 hangs SmartUPS-1400


I purchased a AP9617 off E-Bay as a upgrade from my AP9606 card.

When I tried swapping the cards, the 9617 did not "boot" and hung

my UPS with just the "ONLINE" led flashing.

Pushing "OFF", then releasing just went back to "ONLINE" led flash.

I tried using my serial cable to check UPS, that did not work.

Swapping back to 9606 card everything just fine.

Some info on UPS.

Smart UPS-1400

Firmware 70.9.D

Mfg. date: 12/10/97

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

After a close inspection / comparison with the working AP9617 from my office I found

that one surface mounted component is missing (ripped off card) from my dead card.

The part is labeled C9 / C9A

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

Well done Menkelis ! - you are a pretty resourceful person to be able to fix your own network card in that way and save it from going to the landfill ! Hope the card gives you many years of service.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM


I purchased a AP9617 off E-Bay as a upgrade from my AP9606 card.

When I tried swapping the cards, the 9617 did not "boot" and hung

my UPS with just the "ONLINE" led flashing.

Pushing "OFF", then releasing just went back to "ONLINE" led flash.

I tried using my serial cable to check UPS, that did not work.

Swapping back to 9606 card everything just fine.

Some info on UPS.

Smart UPS-1400

Firmware 70.9.D

Mfg. date: 12/10/97

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

  • How old is the AP9617 (we can tell if you give us the first six characters of its serial number)?
  • When this happens, are there lights on the AP9617, if so, which?
  • Do you have another UPS to try it in?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

AP9617 information

Three stickers found

Backside next to MAC: BA0848001750

Top of card: 1040219900524650

On chip:       8262T/R3.5.8

No lights on AP9617, with and without network cable.

I have read that they should flash as the card boots, which is why I wrote that there was no boot.

This is the only UPS I have with a SmartSlot.  I will check at work to see if there is a spare

UPS that has a SmartSlot so that I can compare.

At this time I have my original AP9606 back in the UPS and it is working just fine, and I can

access the web page.

It acts like something is "holding" the communication bus so that

the UPS does not initialize.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

Yes, I agree. It does sound like a card specific issue but I also was curious if this UPS was so old that it did not work properly with something newer than an AP9606.

You said the model is Smart UPS-1400 - is that what it says on the white sticker on the back or do you see something like SU1400NET? I ask because I suspect Smart-UPS 1400 came from the AP9606 and is not the exact SKU of your UPS. Although, older Smart UPS did have model numbers like that (in the early 90s and yours is from '97) so what is what I am trying to figure out. I could then verify if a UPS this old would work with AP9617. You would think it does but I am not 100% sure based on the symptom you're describing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:02 AM

Yes the message "Smart UPS-1400" cam from the AP9606, and is the label on the front of the UPS.

When I get home after work I will check for another sticker on the back.  The UPS when bought did

not have the AP9606 pre-installed. I bought the card for another UPS that I no longer have, a Smart UPS-700.

I checked at work, and there are APC UPS here but they have keying "tabs" to prevent 9617 from being plugged in.

On the other hand, in our spare's locker there is a AP9617 card that I can borrow overnight and

will see if it also causes my UPS to hang.

I will post back result tomorrow when I get back to work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

Yea, SMT3000RMT's.

Just as a FYI, at home I did a complete shut down of UPS, pulled cord, then pushed "OFF" button

until click.  Then swapped cards.  On plugging in UPS, it went to a "flashing" ONLINE lamp and

that is where it stayed.  The power outlets were hot (bypass mode) which was expected from

the times I have changed battery packs before.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

Sounds good. I presume the UPSs at work are the newer style with LCDs as well.

I look forward to your response and findings smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

The sticker on my UPS says the unit is a SU1400NET.

I put in the 9617 card I borrowed from work, and it works just fine.

So it looks like I have a dead card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

One thing that I haven't seen mentioned in this thread is whether the AP917 card you bought has the correct firmware on it for the "Smart-ups"...it could be wrong and have firmware on it for another family of UPS such as the three phase Symmetra model. If you get signs of life from the card when plugged into the smart slot you can go into the back of the UPS's serial port (DB-9 connector) using the APC cable 940-0024C and using hyperterminal  at 2400 baud  8,N, 1 and see what comes up. When you hit enter you will get a "login" prompt. The id/password might be still the factory "apc" "apc" , if not follow the instructions on the APC knowledge base to reset it to factory ID/password (which is basically to push and hold the reset button when you are at the Login prompt....or for newer firmware cards you push the reset button once, and then once the status led starts flashing you push reset again and wait for the status led to come back on solid (30 -45 seconds). Once you are logged in, the the first things that should show is what the operating system ("AOS") firmware module is,  and what the  "application" module is which should read as being for the "Smart-ups" . Anything else will cause unpredictable results!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

In the very first post, I did try to connect using a serial cable but

The UPS never got to the point in it's self-test where I could continue.

The borrowed 9617 card let the UPS complete self-test and the serial cable

was then active.

I am just going to toss the card as the seller refunded my the $19.00 I paid,

which was an unexpected turn of events.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

0 Likes
0
3247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:40 AM . Last Modified: ‎2024-03-05 02:01 AM

After a close inspection / comparison with the working AP9617 from my office I found

that one surface mounted component is missing (ripped off card) from my dead card.

The part is labeled C9 / C9A

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore