Posted: 2025-02-26 03:34 PM
Hi,
I am trying to figure out what firmware to use and what order to use to upgrade a APC NetShelter Metered Rack PDU by uploading to the devices FTP.
Hardware Factory | |
Model Number: | AP8858EU3 |
Serial Number: | ZAXXXXXXXX |
Hardware Revision: | 2 |
Manufacture Date: | 12/21/2010 |
MAC Address: | XX XX XX XX XX |
Management Uptime: | 1 Day 23 Hours 25 Minutes |
| |
Network Management Card | |
Model Number: | AP9537 |
Serial Number: | ZAXXXXXXX |
Hardware Revision: | 5 |
Manufacture Date: | 12/15/2010 |
| |
Application Module | |
Name: | rpdu2g |
Version: | v5.1.0 |
Date: | Apr 14 2010 |
Time: | 14:50:01 |
| |
APC OS (AOS) | |
Name: | aos |
Version: | v5.1.2 |
Date: | Apr 5 2010 |
Time: | 14:03:27 |
| |
APC Boot Monitor | |
Name: | bootmon |
Version: | v1.0.2 |
Date: | Jan 21 2010 |
Time: | 13:35:57 |
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-27 03:51 AM
Hello,
It seems the Rpdu had NMC 2 embedded ,so you can download the latest version 7.1.4 from the below link under software and firmware section under name (Network Management Card v7.1.4 RPDU 2G Firmware Executable (7.1.4))
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-27 03:51 AM
Hello,
It seems the Rpdu had NMC 2 embedded ,so you can download the latest version 7.1.4 from the below link under software and firmware section under name (Network Management Card v7.1.4 RPDU 2G Firmware Executable (7.1.4))
Regards,
Karim