Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
AP8641 "Component communications lost with Phase Meter"
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-0808:54 PM
AP8641 "Component communications lost with Phase Meter"
I have multiple errors all relating to component communications with the device. The only information that I have been able to locate in the forum says is "Please verify that the terminator in inserted in either the in or out port" which it is. So, because of the disconnect, the display and web interface is just showing 0.0 for everything?
Component communications lost with Phase Meter.
Communications Lost.
Component communications lost with Outlet Board 1 Meter. Please verify that the terminator is inserted in the in or out port.
Component communications lost with Outlet Board 2 Meter. Please verify that the terminator is inserted in the in or out port.
Component communications lost with Outlet Board 3 Meter. Please verify that the terminator is inserted in the in or out port.
So, if the terminator is inserted, is there anything else to do to trouble shoot this?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-1207:47 AM
Besides the terminator, other steps to take would be confirming the unit has the most up to date firmware, or safely reseating the display module to rule out a poor connection. We have more information on those steps here: https://www.apc.com/us/en/faqs/FA168022/