Last night one of the apc's shutdown all ports for several times with intervals of 2 to 6 hours. I got the following errors:
Critical Switched Rack PDU: Internal power supply #1 fault.
Critical Switched Rack PDU: Internal power supply #2 fault.
EDIT:
This has been solved, seems the datacenter had a broken PDU which caused mine to flip. Once replaced all was ok again.
Message was edited by: chrissweden
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:28 AM . Last Modified: 2024-03-14 12:46 AM
Last night one of the apc's shutdown all ports for several times with intervals of 2 to 6 hours. I got the following errors:
Critical Switched Rack PDU: Internal power supply #1 fault.
Critical Switched Rack PDU: Internal power supply #2 fault.
EDIT:
This has been solved, seems the datacenter had a broken PDU which caused mine to flip. Once replaced all was ok again.
Message was edited by: chrissweden
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:28 AM . Last Modified: 2024-03-14 12:46 AM
Last night one of the apc's shutdown all ports for several times with intervals of 2 to 6 hours. I got the following errors:
Critical Switched Rack PDU: Internal power supply #1 fault.
Critical Switched Rack PDU: Internal power supply #2 fault.
EDIT:
This has been solved, seems the datacenter had a broken PDU which caused mine to flip. Once replaced all was ok again.
Message was edited by: chrissweden
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of