AP7900 failed firmware upgrade, bricked my unit -> how to reset?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7900 failed firmware upgrade, bricked my unit -> how to reset?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
7
3291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

AP7900 failed firmware upgrade, bricked my unit -> how to reset?

Hi - I tried a firmware upgrade to 3.73 via TFTP download. First time the AOS download failed but I was able to get back in and try again, the second time it seems to have worked (I got a message indicating the file transfer was successful). At that point the unit was unresponsive and my telnet session froze up. I tried to connect to the serial console, nothing, not even a prompt. So I was never able to download the app image. Tried the password reset procedure but I never get blinking LEDs, just two solid amber LEDs. I also tried powering up with the reset button pressed to see if that would reset the unit, didn't work.

File names are:
apc_hw02_aos_373.bin -> this seems to have downloaded successfully
apc_hw02_rpdu_373.bin -> never downloaded this

Is there any way to reset the unit to factory defaults? I'd think there must be a way to recover from corrupted downloads. Please help!

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

yeah there is no procedure like that on these. on our new PDUs due out shortly and our Network Management Card 2 based devices, there is a recovery mode.

if you have power cycled it and waited for several minutes before reapplying power, then i do think it is hosed. while the card was writing to its SRAM, something my have happened.

power cycling was the greatest possibility of trying to get it to a state where we could at least FTP to it and sort of finish the upgrade.

can you tell me the first several digits of your serial number and we'll see if its in warranty? something like ZA0732 it should start with?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

Thank you for sharing with us. That sounded familiar and I thought I had it indicated in a knowledge base.

I had it here (how to upgrade a single card) -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US

I will go ahead and add that same note to the kbase we have on mass upgrades (How do I perform a mass firmware upgrade on APC network enabled products? | FAQs | Schneider Electri...). Had you referred to that?

Or basically, where can I document it besides your post to assist other users that may run into this issue? Just trying to think how a user might come across this to prevent issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

Thank you for the response Angela and for your help with the support case.

We searched around via Google, and via the APC support knowledge base, and via this support forums but could not find the information about the 11 character username and password limit in the NMC Upgrade Utility.  We didn't know we were looking for a username/password truncation issue so we were looking for issues about the firmware upgrade failing halfway through the process.

At the time we were searching via Google for

   "AP7900 firmware upgrade fails"

   "AP7900 firmware Could not login"

and that is how we ended up at this article

If there were an KB or FAQ article with a title something like "NMC Upgrade Tool firmware update fails with Could not Login on username or password longer than 11 characters" we might have had more luck finding it.

Of course just fixing the problem of truncation in the NMC Upgrade Tool would be great - the funny thing is the tool's first login to FTP works, it is the login after the reboot that fails, so there is some part of the codebase that can handle longer than 11 characters. Barring that another thing that might help is if the NMC Upgrade Tool gave a warning about the username/password truncation issue (and/or detected if user was about to have the problem) and/or if the NMC Upgrade Tool shipped with a text file of known limitations/issues. There are also release notes with the firmware that we did read through that might have mentioned the issue.

Seeing the FAQ articles the information on username/password truncation is definitely there on the FAQ about upgrading:

*In NMC1 Upgrade Utility v1.2 or higher, a username or password longer than 11 characters will be truncated. Thus, you will need to change the password to 11 characters or less or choose another firmware upgrade method. Reference the picture below on how to check your NMC Upgrade tool version.

Note: *In NMC1 Upgrade Utility v1.2 or higher, a username or password longer than 11 characters will be truncated. Thus, you will need to change the password to 11 characters or less to use upgrd_util.exe. This could be modified using a mass configuration first, outlined in knowledge base FA156117. Reference the picture below on how to check your NMC Upgrade tool version.


Thanks again Angela.

-Michael


Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

Raising this thread from the dead because it helped me un-brick my AP7900.

Upgrading to 3.74 looked good; the installer detected old enough firmware to know it had to do two upgrades; first one worked, second one didn't (Status LED flashing green/amber).

Power failed, Status green, but Overload LED with 0 amps (nothing plugged in). Could ping AP7900 but not Telnet or web to it. Was able to FTP in with apc/apc (whew!) and saw apc_hw02_aos_374.bin, but no apc_hw02_rpdu_374.bin, similar to what OP found above. FTP put apc_hw02_rpdu_374.bin and Overload LED immediately changed to OK!

Web'd in using apc/apc, reset everything the way it was and all seems to be working ok.

Just paying it forward, hope this helps someone!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

hi brian,

can you tell us what LEDs we have now around the RJ-45 network jack on the PDU? I hope that I can help you with this it may just take some tinkering.

can you tell me what the old firmware version was that you were trying to upgrade from?

can we FTP to the card? if not, you can try power cycling the PDU for 5-10 seconds and giving it a few minutes to boot up. if its in production, see if you can press the "reset" button on the PDU display with a paper clip to reboot the management interface only.

if you can FTP, do an ls command and tell me what .bin files you see listed.

thanks!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

When I power on the two LEDs on the RJ45 are solid amber (orange) and they never change colors. The LED near the display indicates Overload, this also never changes unless the unit is powered off. Doesn't matter if the RJ45 is connected or if the console is connected. When I press the reset button with a paper clip the Overload LED stays on but the two amber LEDs go off. As soon as I release the reset button the amber LEDs come back on and nothing else happens.

I think the old AOS version was either 2.64 or 2.65 and the app version was either 2.64 or 2.65. Can't say with 100% confidence, but it was definitely greater than 2.02.

I can't even ping the unit, let alone telnet or FTP. There are no blinking LEDs on the switch I have it connected to... the link is totally down and never comes up. I have power cycled many times and waited plenty of time. The PDU appears to be doing nothing, it's not booting, and there's no console output. I have tried 9600 and 2400 bps many times.

I think I'm hosed without some kind of recovery procedure built into the hardware. For example on a Cisco 871 router you can power cycle with the reset button pressed (with a paperclip) for 30 seconds and the router will clear it's flash memory and dump you to a boot loader prompt. I tried this with the PDU and kept the reset button pressed for more than 2 minutes. There seems to be no boot loader prompt.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

yeah there is no procedure like that on these. on our new PDUs due out shortly and our Network Management Card 2 based devices, there is a recovery mode.

if you have power cycled it and waited for several minutes before reapplying power, then i do think it is hosed. while the card was writing to its SRAM, something my have happened.

power cycling was the greatest possibility of trying to get it to a state where we could at least FTP to it and sort of finish the upgrade.

can you tell me the first several digits of your serial number and we'll see if its in warranty? something like ZA0732 it should start with?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
3279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:31 AM . Last Modified: ‎2024-03-14 12:43 AM

Hi - I tried a firmware upgrade to 3.73 via TFTP download. First time the AOS download failed but I was able to get back in and try again, the second time it seems to have worked (I got a message indicating the file transfer was successful). At that point the unit was unresponsive and my telnet session froze up. I tried to connect to the serial console, nothing, not even a prompt. So I was never able to download the app image. Tried the password reset procedure but I never get blinking LEDs, just two solid amber LEDs. I also tried powering up with the reset button pressed to see if that would reset the unit, didn't work.

File names are:
apc_hw02_aos_373.bin -> this seems to have downloaded successfully
apc_hw02_rpdu_373.bin -> never downloaded this

Is there any way to reset the unit to factory defaults? I'd think there must be a way to recover from corrupted downloads. Please help!

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of