Hi. I inherited 5 AP7863s that the password has been changed to something but apc-apc. I know the IP and can connect via Ethernet cable and get login, but can't guess what the user/password is. The reset button resets the PDU's interface but apparently not the pw. Any way to reset it?
thanks
-robotz
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-18 12:16 AM
Hello,
You'll need the 940-0144 DB-9 to RJ-12 configuration cable that these Rack PDUs use along with a computer with a DB-9 serial port or working serial to USB adapter. When you have that, refer to the Network Management Card 1 (NMC1) password reset procedure outlined here in order to reset it -> Network Management Card Password Reset Procedure | FAQs | Schneider Electric US
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-18 12:16 AM
Hello,
You'll need the 940-0144 DB-9 to RJ-12 configuration cable that these Rack PDUs use along with a computer with a DB-9 serial port or working serial to USB adapter. When you have that, refer to the Network Management Card 1 (NMC1) password reset procedure outlined here in order to reset it -> Network Management Card Password Reset Procedure | FAQs | Schneider Electric US