Model identification 0G-9354-01

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Model identification 0G-9354-01
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
16
6349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Model identification 0G-9354-01

Hello,

Can someone help me to identify the model of this unit? (see attached screenshot)

It seems to be the model 0G-9354-01 but in the support section of apc.com site seems it does not exists.

Does somebody know if there are firmware updates available?

Thank you in advance

Michele

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

This is the model number of a "brain" for an ISX PDU. I don't know what particular model it will be to be honest.

Yes, there is a firmware upgrade available for the XRDP app - AOS 3.7.5, XRDP 3.7.2. The download SKU is SFPDUM372.

You can find it @ http://www.apc.com/tools/download/index.cfm under Firmware Upgrades - Modular Power Distribution. Or, since you're using ISX Central, I believe it should show in the upgrade catalog that device offers as this firmware was released, March, 2013.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Hi again.

Download this firmware file: ftp://restrict:Kop$74!@ftp.apcc.com/restricted/hardware/nmcard/firmware/px2/377/apc_hw03_aos390_px23... 

Launch the .exe which is pretty straight forward but specifically, you can review any of the NMC1 firmware upgrade options here http://www.apc.com/us/en/faqs/FA156047 

It is OK to do this while the UPS is on and operating.

You'll ultimately only have an update to the AOS component which brings TLS 1.0 and some other little fixes. Your application file will be the same (but still needs to be upgraded as part of the process).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

This is the model number of a "brain" for an ISX PDU. I don't know what particular model it will be to be honest.

Yes, there is a firmware upgrade available for the XRDP app - AOS 3.7.5, XRDP 3.7.2. The download SKU is SFPDUM372.

You can find it @ http://www.apc.com/tools/download/index.cfm under Firmware Upgrades - Modular Power Distribution. Or, since you're using ISX Central, I believe it should show in the upgrade catalog that device offers as this firmware was released, March, 2013.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Thank you very much Angela for your support.

Have a nice day

Michele

Reply

Link copied. Please paste this link to share this article on your social media post.

Benji_apc
Ensign Benji_apc
Ensign

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

I am also looking for the current firmware release, could you help me out?

One of our Symmetra units has 3.7.5 while the other one has 3.7.8, in the download section I can only find 3.7.2 in Modular Power Distribution.

Also is there some information when the new 0G-9354A (based on NMC2) was released?
One of the Symmetras is kind of new, but we received it feels like it was shipped with an ancient card...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:57 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Hi Benjamin - I can shed a little light on this.

From what you're saying, you are interested in Symmetra firmware right, not modular PDU (with 0G-9354-01)?

If so, 0G-9354 latest rev I see is AOS 3.9.0 with px2 app v3.7.7. Here is a link. ftp://restrict:Kop$74!@ftp.apcc.com/restricted/hardware/nmcard/firmware/px2/377/apc_hw03_aos390_px23... 

Now, 0G-9354A is our Network Management Card 2 brain for Symmetra PX (100, 160, etc) models. It started shipping in supported models units manufactured in 2017. (You can check your UPS's serial number - refer to the first six characters. It should be something like PD1703. 17 refers to the year in my example. If yours says 16, then it was manufactured last year and thus probably came with 0G-9354.)

0G-9354A replaces 0G-9354 (Network Management Card 1) as you've found. You can apply for an upgrade to this second generation card/brain through your local support team, especially if you just received your UPS unit.

If you do proceed, let me know if you run into any troubles trying to get 0G-9354A for your new UPSs..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Angela.

My company just bought a Symmetra PX100   Unforunately, we don't have the cable to program the NMC that came with it.   We have a 0G-9354 and in your earlier post you mentioned that it should be a 0g-9354A.    How do I go about getting a replacement? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Hi Thomas,

The programming of the IP address for the 0G-9354 can be done through the UPS's powerview display actually if that is all you're looking to do. Cable is not needed specifically for that.

0G-9354 is fine to use. Unless you need an second generation NMC for any specific reason or special feature, you can continue along with 0G-9354. If you do determine you need a replacement, you should be able to just contact technical support and ask about getting a 0G-9354A. They'll need your UPS serial number to start with.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

I am impressed with the speed of your reply!   Thank you.   That will give us what we need for the time being!   

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

You're welcome! (Sorry, this reply was slow with traveling and craziness! winklaughing) .. Happy Thanksgiving!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

One more question!  πŸ™‚   

How do we go about updating the firmware?   

Hardware Factory

Model Number: 0G-9354
Serial Number: QD1702111671
Hardware Revision: 0C
Manufacture Date: 01/13/2017
MAC Address: 00 C0 B7 DB 40 51
Management Uptime: 0 Days 1 Hour 2 Minutes

Application Module
Name: px2
Version: v3.7.7
Date: 06/03/2014
Time: 20:24:48

APC OS (AOS)
Name: aos
Version: v3.7.8
Date: 06/03/2014
Time: 18:02:25

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Hi again.

Download this firmware file: ftp://restrict:Kop$74!@ftp.apcc.com/restricted/hardware/nmcard/firmware/px2/377/apc_hw03_aos390_px23... 

Launch the .exe which is pretty straight forward but specifically, you can review any of the NMC1 firmware upgrade options here http://www.apc.com/us/en/faqs/FA156047 

It is OK to do this while the UPS is on and operating.

You'll ultimately only have an update to the AOS component which brings TLS 1.0 and some other little fixes. Your application file will be the same (but still needs to be upgraded as part of the process).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Once again, you are the best.   πŸ™‚ 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:17 AM

Angela, 

It appears the NMC that we have 0G-9354 model NMC, which only supports an older firmware that our systems can't support.   Can you please provide a point of contact for me to upgrade our NMC to the -A model? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

Hello!

Our company has Symmetra PX 160 with 0g-9354A.
the web displays the message "Local Management-To-UPS Communication Lost". After replacing the monitoring card,  problem remains.

Network Management Card AOS v6.5.0

Will the firmware update help?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

Hi,

What firmware is on the card now? You will find that information under the About tab.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

nuPIHiKxJIAvvmPDpObKAQ%3D%3D.pngnuPIHiKxJIAvvmPDpObKAQ%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

0 Likes
0
6350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:58 AM . Last Modified: β€Ž2024-03-18 12:16 AM

Hi,

I checked with the 3 Phase support team in North America and they recommend you call local support for assistance. Local support information will be found at this link.

https://www.apc.com/us/en/support/contact-us/index.jsp

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore