AP7723 showing wrong model and voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7723 showing wrong model and voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:03 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
11
2738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:03 AM . Last Modified: ‎2024-02-14 11:13 PM

AP7723 showing wrong model and voltage

I have an AP7723, which is connected to a 208V input on source A with no load currently.

It is showing the error messages: 

    fault exists on source a

    Under voltage violation on source A

On the Unit tab - Measurements it shows:

    Input voltage: source A 105

    -12V PS: -23 VDC

in Status it shows:

    -12V PS: OK

in About ATS it shows:

    Model: AP7752
    Firmware Revision: 2.0.3
    Firmware Date: 9/08/10
    Hardware Revision:
    Manufacture Date: DD/MM/YYYY
    Serial Number:

in Administration - General - About:

  Hardware Factory
    Model Number: AP7723
    Serial Number: 5A1137T06596
    Hardware Revision: 01
    Manufacture Date: 09/09/2011
    MAC Address: 00 C0 B7 24 61 83
    Management Uptime: 0 Days 7 Hours 58 Minutes
  Application Module
    Name: g2ats
    Version: v3.9.0
    Date: 06/16/2015
    Time: 16:37:24
  APC OS (AOS)
    Name: aos
    Version: v3.9.0
    Date: 05/11/2015
    Time: 14:45:05

Any help with this would be appreciated.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • 208v
  • ap7723
  • ats
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

0 Likes
0
2738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

Yeah, we don't repair this product even in warranty, only full unit replacement. Since it appears out of warranty, then we'd have to suggest purchasing a replacement. The DIMM module/controller Terry speaks of is not user replaceable and replacing it may cause other problems. We also aren't sure how the controller got to this state and if there is another fault somewhere the caused it to revert to reporting the wrong model.

While, if you've got nothing to lose, it may be worthwhile to tinker at your own risk (if you can find a module) but I know that we (APC) will not sell or give you this ATS Controller part/module.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

Hi Benjamin,

The one serial number I do see indicates the ATS was manufactured in 2011. Was this unit in service and recently this problem started or was it new out of the box? Or purchased used? Basically, what has happened prior to you noticing this issue and what is the background? What serial number is on the unit itself on the white sticker? I'd guess the one you see under Administration tab?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

Hello Angela,

This is a unit that we received used and the serial number on the unit matches the number on the administration tab.

I noticed that in about ATS it showed the wrong model and an old firmware.

I just updated the firmware to version 3.9.0 as shown in the administration section.

I was wondering if there was some way to update the firmware referenced in the about ATS section.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

Hi Benjamin,

The AOS 3.9.0/gt2ats 3.9.0 Network Management Card firmware you updated has the ATS microprocessor's firmware embedded in it. v2.0.3 (and in newer hardware 3.0.5) are the latest versions and are equivalent to each other logic wise. So, you're at the latest versions. The management card is what you log into which retrieves data from the ATS microcontroller. The ATS microcontroller is the heart of the ATS logic and the management card is for the user to monitor the ATS. They have separate firmwares as you know.

I'm not sure what happened here but somehow, the ATS microcontroller is messed up and typically, this would require an ATS replacement unfortunately. There is no way for the user to re-program the model number and this is only done at the factory. This can happen due to a weird surge or fault or perhaps a previous botched firmware upgrade.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

Thank you for your response and help in understanding what the exact problem is.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

Hi Benjamin, no problem. Sorry I don't have better news. yell

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

I wonder if the "warranty void if removed" sticker is intact on the unit. The ATS microcontroller is on a socketed DIMM-type module on the main power control board. It is possible that the seller swapped one from another unit to try to turn 2 non-working units into 1 good unit and didn't realize that there were configuration parameters stored in there as well. I would expect a fault or failed microcontroller firmware upgrade to either make the microcontroller completely non-responsive or to put it in a fail-safe download mode where the next attempt to flash the NMC would also download new microcontroller firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

I had it in my mind that somehow by default, every ATS microcontroller starts as an AP7752 - or if it loses its configuration, instead of going to 0000 or ----- it says AP7752 but I am second guessing myself now. Good suggestions and feedback terry. I agree with your last sentence too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

0 Likes
0
2739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:13 PM

I will check on the tamper-evident sticker next time I am in front of the hardware. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

0 Likes
0
2739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

I have checked, and the seals are still intact. Do either of you know of any out of warranty repair solutions for these devices. The only things I found online specified UPS devices.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

0 Likes
0
2739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

It probably isn't cost-effective. I suspect that a lot of the UPS repairs are being done because the customer has a lot of that specific UPS and wants to maintain that (and not deal with slightly different outlet positions, rackmount hardware, etc.). If you can find a damaged AP7723 (case bent, outlets broken, etc.) you should be able to take the ATS microcontroller module out of it and install it in your existing unit. As I posted earlier, it is socketed in a DIMM-type socket. Obviously do this with all of the power unplugged and only if you feel confident doing that sort of work.

You might be able to get the part number off of the module (it will probably be something like nnn-nnnn) and call APC. Sometimes you'll get someone who will send you an oddball part - it seems to depend on who you get along with what the inventory for the specific part is. Unlikely to work, but you could give it a try.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

0 Likes
0
2739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:04 AM . Last Modified: ‎2024-02-14 11:12 PM

Yeah, we don't repair this product even in warranty, only full unit replacement. Since it appears out of warranty, then we'd have to suggest purchasing a replacement. The DIMM module/controller Terry speaks of is not user replaceable and replacing it may cause other problems. We also aren't sure how the controller got to this state and if there is another fault somewhere the caused it to revert to reporting the wrong model.

While, if you've got nothing to lose, it may be worthwhile to tinker at your own risk (if you can find a module) but I know that we (APC) will not sell or give you this ATS Controller part/module.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore