AP7723: "Communication has been lost to the device"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7723: "Communication has been lost to the device"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
4
2654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

AP7723: "Communication has been lost to the device"

Hello,

My AP7723 blinks with the LED sequence (left to right) on front panel. When I log to management via HTTP I got:

q115SD6mQZ8Dq%2FPA8UFMAQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngq115SD6mQZ8Dq%2FPA8UFMAQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

AbY4K4sxPcJqFLkmZFievg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngAbY4K4sxPcJqFLkmZFievg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

I made the firmware upgrade about 2 months ago - but the device was fine after procedure. Maybe now during the disconnect of both power sources it restarted and got some problems with the communication with ATS or firmware issue?

Reset to the factory default or full restart by disconnect of the primary and secondary inputs did not help.

Please advice if there is any workaround or (even unsupported) way of fixing the device?

Thank you,

Matt

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

I landed here, because i had the same problem.  I took mine apart and re-seated the ATS daughter card.  Because I tried the firmware first, the ATS didn't come up immediately as the event log now showed it upgrading firmware.  

HOWEVER, there are charged capacitors in there, so unless you know what you're doing, it's not a good idea that you take the cover off and service your own equipment.   Enter at your own risk. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

I assume that this device isn't powering any loads at present and that it is OK to disconnect it from both AC input sources? If not, don't do anything that could make a bad situation worse until you can schedule an outage. Needless to say, if this unit is under warranty, you should just contact APC to get a replacement unit.

There are two separate microcontrollers in the unit - a large, complicated one that implements the network management card functionality (the aos and g2ats app) and a small, simpler one that handles the actual ATS function. As part of a firmware update on the NMC, when the g2ats app boots it tries to establish communication with the ATS microcontroller. Once it succeeds, it checks the ATS microcontroller firmware revision and if it is lower than the revision bundled in the g2ats app, it tries to download the new firmware to the ATS.

The picture you attached seems to show a very confused management card that can't communicate with the ATS microcontroller and seems to be trying to repeatedly download firmware to the ATS.

I would suggest disconnecting the unit from both power sources, letting it sit for a minute or two, then connect a single power source and attempt to update the NMC firmware (latest is 3.9.2 for both aos and g2ats, and can be found on the main APC site). Let it update (it will reboot a few times) and see if it can establish a connection to the ATS after it has the latest firmware. Once it notices that the ATS has older firmware, it will attempt to download the newer firmware (the 2-digit 7-segment display will probably show something like "dl" during this process).

The microcontroller for the ATS is on a daughterboard inside the chassis, but I would not recommend opening the chassis. Aside from dangerous voltages, there is no source for spare microcontroller daughterboards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

Thank you Terry for your advice.

I followed the sequence:

1. disconnect all power sources and let it rest for 5 minutes

2. update the firmware 

3. Let it restart

4. logged back

5. I got the following error:

09/05/2017 23:21:26 Automatic Transfer Switch: ATS Controller firmware download failed.
09/05/2017 23:21:26 Automatic Transfer Switch: ATS Controller firmware download begun.
09/05/2017 23:20:25 System: Web user 'apc' logged in from x.x.x.x.
09/05/2017 23:19:36 Automatic Transfer Switch: 7-Segment display hardware failure.
09/05/2017 23:19:36 Automatic Transfer Switch: Phase Leds/Push-button hardware failure.
09/05/2017 23:19:36 System: Data Log cleared.

device is not under warranty - please let me know if I can do anything about it to fix it.

Mat

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

I think you'll need to take this up with APC support to see if they have any suggestions for you. It seems that the ATS microcontroller (not the management card) never booted in the first place, so attempts to download newer firmware are failing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

I landed here, because i had the same problem.  I took mine apart and re-seated the ATS daughter card.  Because I tried the firmware first, the ATS didn't come up immediately as the event log now showed it upgrading firmware.  

HOWEVER, there are charged capacitors in there, so unless you know what you're doing, it's not a good idea that you take the cover off and service your own equipment.   Enter at your own risk. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore