AP7953 - SNMP Outlet state/change

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7953 - SNMP Outlet state/change
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
3
2516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

AP7953 - SNMP Outlet state/change

Hi All, 

Just inherited a 7953 and trying to get it configured. The biggest hurdle is that the web interface doesn't support TLS1.2 or SSL3 so thats not accessible in Chrome, etc.

I thought it would therefore be easier to use SNMP and a php script as the only control I need is to turn on/off sockets. 

Got the PDU setup and I can access SNMP but I am not seeing anything related to the outlet state, which from the MIB should be PowerNet-MIB::rPDUOutletStatusOutletState.

Is there something I need to do to allow this, or that needs to be activated?

Hardware Factory
   
Model Number: AP7954
Serial Number: xxxxxxxxx
Hardware Revision: B2
Manufacture Date: 06/21/2006
MAC Address: xxxxxxx
Management Uptime: 0 Days 2 Hours 20 Minutes

Application Module
   
Name: rpdu
Version: v3.9.2
Date: 07/07/2016
Time: 10:40:30

APC OS (AOS)
   
Name: aos
Version: v3.9.2
Date: 07/06/2016
Time: 15:12:05

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:24 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:24 AM . Last Modified: ‎2024-02-14 11:01 PM

Thanks for looping back and sharing what you found.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

Hi Thomas,

You're in the right area in our SNMP MIB. Are you able to do a walk the PDU at all?

SNMPv1 is enabled on the PDU by default but if you inherited it, perhaps it is disabled or incorrectly configured? Check under Administration tab->Network sub tab->SNMPv1 configuration in the web. (Seems like you were maybe in the web at some point to copy/paste that firmware info though you said HTTPS wasn't working in modern browser. SNMP config can also be checked via Telnet/SSH or local serial console.) If you want to use SNMPv3, that can be turned on and you just have to configure it.

If you verify SNMPv1 or SNMPv3 is enabled and configured with community strings and access control settings, then I'd try a walk from the top of the MIB on the PDU and see what comes back.

The control outlet OID is here: .iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU.rPDUOutlet.rPDUOutletControl.rPDUOutletControlTable.rPDUOutletControlEntry.rPDUOutletControlOutletCommand

Then, you just will have to specify an SNMP instance on that OID (to indicate which outlet you want to control). Here is the description on that OID:

Getting this variable will return the outlet state. If
 the outlet is on, the immediateOn (1) value will be returned.
 If the outlet is off, the immediateOff (2) value will be
 returned.
 Setting this variable to immediateOn (1) will immediately turn
 the outlet on.
 Setting this variable to immediateOff (2) will immediately turn
 the outlet off.
 Setting this variable to immediateReboot (3) will immediately
 reboot the outlet.
 Setting this variable to delayedOn (4) will turn the outlet on
 after the rPDUOutletConfigPowerOnTime OID time has elapsed.
 Setting this variable to delayedOff (5) will turn the outlet off
 after the rPDUOutletConfigPowerOffTime OID time has elapsed.
 Setting this variable to delayedReboot (6) will cause the
 Switched Rack PDU to perform a delayedOff command, wait the
 rPDUOutletConfigRebootDuration OID time, and then perform a
 delayedOn command.
 Setting this variable to cancelPendingCommand (7) will cause any
 pending command to this outlet to be canceled.

rPDUOutletStatusOutletState is a read only OID to get the current outlet state. You'll want to use the OID I shared above to control the outlets. 

If you have outlet groups you want to control, I think you can use that same OID somehow if you issue a command to one of the outlets in the same group (I'd have to do a walk on a device with groups to confirm that).

In addition to SNMP, we have a special CLI available via Telnet/SSH/serial connection that may be of help for scripting outlet control. Check here for more info and how to access -> http://www.apc.com/us/en/faqs/FA156163

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:23 AM . Last Modified: ‎2024-02-14 11:01 PM

Shortly after I posted this I figured out what was going wrong. 

I ran snmpwalk with the first OID defined to run through the whole list:

snmpwalk -v 3 -l authNoPriv -u "wsername" -a MD5 -A "Pa55Word!" xxx.xxx.xxx.xxx .1.3.6.1.4.1.318

This then returned all the details for the device:

SNMPv2-SMI::enterprises.318.1.1.4.1.1.0 = STRING: "B2"
SNMPv2-SMI::enterprises.318.1.1.4.1.2.0 = STRING: "v3.9.2"
SNMPv2-SMI::enterprises.318.1.1.4.1.3.0 = STRING: "06/21/2006"
SNMPv2-SMI::enterprises.318.1.1.4.1.4.0 = STRING: "AP7954"
SNMPv2-SMI::enterprises.318.1.1.4.1.5.0 = STRING: "xxxxxx"
SNMPv2-SMI::enterprises.318.1.1.4.2.1.0 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.1.4.2.2.0 = STRING: "On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  On  "
SNMPv2-SMI::enterprises.318.1.1.4.2.3.0 = STRING: "No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  No  "
SNMPv2-SMI::enterprises.318.1.1.4.3.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.4.3.2.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.4.3.3.0 = STRING: "pdu1.cwcs.co.uk"
SNMPv2-SMI::enterprises.318.1.1.4.4.1.0 = INTEGER: 24
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.5 = INTEGER: 5
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.6 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.7 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.8 = INTEGER: 8
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.9 = INTEGER: 9
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.10 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.11 = INTEGER: 11
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.12 = INTEGER: 12
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.13 = INTEGER: 13
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.14 = INTEGER: 14
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.15 = INTEGER: 15
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.16 = INTEGER: 16
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.17 = INTEGER: 17
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.18 = INTEGER: 18
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.19 = INTEGER: 19
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.20 = INTEGER: 20
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.21 = INTEGER: 21
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.1.22 = INTEGER: 22
...

I have tried to load the MIB into my test Ubuntu server, but its not having it, keeps returning "Cannot adopt OID in PowerNet-MIB: .." but continues and the OIDs are returned in the format I am familiar with:

iso.3.6.1.2.1.1.9.1.3.1 = STRING: "The MIB Module from SNMPv2 entities"
iso.3.6.1.2.1.1.9.1.3.2 = STRING: "SNMP Management Architecture MIB"
iso.3.6.1.2.1.1.9.1.3.3 = STRING: "Message Processing and Dispatching MIB"
iso.3.6.1.2.1.1.9.1.3.4 = STRING: "USM User MIB"
iso.3.6.1.2.1.1.9.1.3.5 = STRING: "VACM MIB"
iso.3.6.1.2.1.1.9.1.4.1 = Timeticks: (0) 0:00:00.00
iso.3.6.1.2.1.1.9.1.4.2 = Timeticks: (0) 0:00:00.00
iso.3.6.1.2.1.1.9.1.4.3 = Timeticks: (0) 0:00:00.00
iso.3.6.1.2.1.1.9.1.4.4 = Timeticks: (0) 0:00:00.00
iso.3.6.1.2.1.1.9.1.4.5 = Timeticks: (0) 0:00:00.00
iso.3.6.1.2.1.2.1.0 = INTEGER: 2
iso.3.6.1.2.1.2.2.1.1.1 = INTEGER: 1
iso.3.6.1.2.1.2.2.1.1.2 = INTEGER: 2
iso.3.6.1.2.1.2.2.1.2.1 = STRING: "LOOPBACK"
iso.3.6.1.2.1.2.2.1.2.2 = STRING: "lance"
iso.3.6.1.2.1.2.2.1.3.1 = INTEGER: 24
iso.3.6.1.2.1.2.2.1.3.2 = INTEGER: 6
iso.3.6.1.2.1.2.2.1.4.1 = INTEGER: 1500
...

Which I can then work. The above is something to do with the OS and not the APC device. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:24 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:24 AM . Last Modified: ‎2024-02-14 11:01 PM

Thanks for looping back and sharing what you found.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of