AP4421 Source B not available
  • AP4421 Source B not available
Grex_apc
Grex_apc
Cadet
Posted: ‎2021-07-09 04:36 AM . Last Modified: ‎2024-02-14 10:16 PM
1254
after the overvoltage protection has been triggered, the Source B does not come up anymore. If I put the cable on source B, there is a "click" noise, and I checked after switchting the protection to "on" the voltage with measurement, it is 230V.
I aloso tried to use the same circuit, bot the Source B seems to be dead... And maybe it was fault that the overvoltage protection has been triggered.
Can I something try, before replace the whole unit? (maybe there is a broken fuse in it?)
Thanks!
B-DoubleE_apc
Commander B-DoubleE_apc
Commander
Hi Gregor,
Was there a surge or power event that happened on the input side of Source B? Could you share the log files from the ATS? Instructions on where to download can be found here: http://www.apc.com/us/en/faqs/FA156131/
B-DoubleE_apc
Commander
Hi Gregor,