ACRP100 OUT HEAT EXCHANGER FAN

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRP100 OUT HEAT EXCHANGER FAN
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:10 AM

0 Likes
2
913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:10 AM

ACRP100 OUT HEAT EXCHANGER FAN

HELLO

Does anybody knows why the CONDENSER FAN of a ACRP100 stop running and never come back running again?, i have tow of these installed, and the both have fail!, does the vfd of fan has a factory problem or is something that i´m missing?

here is the partnumber of the one that i have : ACCD75201

I´ve change it the first time! that it fails, the units runs for over 4 month and fails again yesterday.
i aplied voltage to the fan and it didn´t start
i´ve jump the VFD control and it didn´t start


thanx

Carlos

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:09 AM

0 Likes
0
913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:09 AM

Carlos,

The condenser for the InRow RP, typically the LNE-S01-A009, uses a JCI P352 PN controller to dictate when the fans turn on. This is a pressure transducer driven fan controller; As your discharge pressure increases, it will cause the controller start the fan. The typical settings for the controller are as follows: 240psi pressure, 70 throttle range, 0 minimum. Perhaps that is the "variable frequency drive" you're speaking of. I'm curious to see how you applied voltage to attempt to start the condenser fan? What pins did you jump? Any further clarification you can provide could be beneficial. If the unit is currently under warranty, I recommend that you contact our technical support team at 888-695-6500 to set up a dispatch.

-Jonathan

Message was edited by: jcas

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:09 AM

0 Likes
0
914
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:09 AM

Checking with our Air Support team. One of the Air members or myself will respond shortly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:09 AM

0 Likes
0
914
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:45 AM . Last Modified: ‎2024-03-18 04:09 AM

Carlos,

The condenser for the InRow RP, typically the LNE-S01-A009, uses a JCI P352 PN controller to dictate when the fans turn on. This is a pressure transducer driven fan controller; As your discharge pressure increases, it will cause the controller start the fan. The typical settings for the controller are as follows: 240psi pressure, 70 throttle range, 0 minimum. Perhaps that is the "variable frequency drive" you're speaking of. I'm curious to see how you applied voltage to attempt to start the condenser fan? What pins did you jump? Any further clarification you can provide could be beneficial. If the unit is currently under warranty, I recommend that you contact our technical support team at 888-695-6500 to set up a dispatch.

-Jonathan

Message was edited by: jcas

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore