ACRD602P ALARMS

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

ETCO
Crewman
Crewman
0 Likes
4
458

ACRD602P ALARMS

We have an ACRD602P cooling unit in a datacenter that frequently gives these alarms:

 

- Humidifier Low Water Condition

- Humidifier Error Tolerance Exceed Condition

 

Knowing that three units of this type installed in datacenter and this is the only one gives this alarm.

 

Please any advice to solve the problem.

Tags (1)
4 Replies 4
EduardoE
Crewman Crewman
Crewman
0 Likes
3
450

Re: ACRD602P ALARMS

Have You checked the water supply line for the humidifier to see if it's receiving water pressure, from the city water? What is the current humidity value? And setpoint? In order to better assist You on this one.

Tags (1)
ETCO
Crewman
Crewman
0 Likes
2
429

Re: ACRD602P ALARMS

Hi,

 

The Humidifier and Dehumidifier were disabled but we always get these alarm, the unit was working from 2018 and there is no problem, a couple of weeks ago we start getting these messages.

Tags (1)
EduardoE
Crewman Crewman
Crewman
0 Likes
1
404

Re: ACRD602P ALARMS

Please reach us at:  877-287-7835 (Opt. 2 Opt. 2). Cooling Technical Support In order to better troubleshoot this.

Tags (1)
EduardoE
Crewman Crewman
Crewman
0 Likes
0
377

Re: ACRD602P ALARMS

Hello Mahmoud. The case# 84499130 has been created for You. I'll reach You by email. For follow up. 

Tags (1)