Posted: 2021-06-28 06:41 AM . Last Modified: 2024-03-18 01:11 AM
Hi Folks,
I wanted to pull in some of the values off of the ACRC100 colling unit via SNMP. I have the PowerNet MIB, and I've done a walk of the device but I'm having trouble identifying some of the values. Specifically I'm looking to retrieve a value from SNMP that provides the power consumption of the unit in kw. It looks like it's available in the web ui, but I can't seem to match that up with an oid. Any suggestions? Thanks.
Just a single unit. I'll retrieve the values of both and see if they match up against what I'm seeing in the UI. Again thanks so much. ![]()
hello. information for this unit via SNMP for device type things on this cooling unit is located under .iso.org.dod.internet.private.enterprises.apc.products.hardware.airConditioners.airIR
It seems like most of the info would be under that within airIRRC sub tree under airIR. What value is it called in the web UI? I see "Cool Demand" but I am not sure if that is what you mean.
Thanks Angela! I'm basically looking for how many kw this unit is consuming. I think the "Cool Demand" is the right field, and if I look at the tree as you suggested, it could be the following oid's: 1.3.6.1.4.1.318.1.1.13.3.2.2.2.3 and 1.3.6.1.4.1.318.1.1.13.3.2.1.1.2 but I'll have to pull the values and see if that match up with what the UI is saying. Thanks for your quick response!
You're welcome. I work with the network management devices and SNMP but not so much in this application with cooling units.
Do you have multiple units in a group? Sounds like you should use 1.3.6.1.4.1.318.1.1.13.3.2.2.2.3 if you just have a standalone unit and then 1.3.6.1.4.1.318.1.1.13.3.2.1.1.2 if you want to know the demand of your entire group.