Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

A single UPS with two VMware stand-alone Hosts

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A single UPS with two VMware stand-alone Hosts
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
fmatsde
fmatsde
Cadet

Posted: ‎2024-10-21 08:29 AM . Last Modified: ‎2024-10-21 08:36 AM

0 Likes
0
360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 08:29 AM . Last Modified: ‎2024-10-21 08:36 AM

A single UPS with two VMware stand-alone Hosts

Hello,

 

we are trying to get a customers UPS running, the situation is as follows. We've got 2 stand-alone VMware Hosts without vCenter and we have got a single UPS (APC Smart-UPS 2200IC) with NMC.

 

After I have configured NMC and installed PowerChute as VM on the first VMware Host, ran the PowerChute Setup Wizard and so on, PowerChute identifies and uses all the VMs running on VMware Host Nr.1 correctly BUT a soon as i install PowerChute as VM on the second VMware Host, i end up with the PowerChute Agent entries on PowerChute VM 1 and with just a single entry on PowerChute VM 2 and on NMC, all the correct entries from PowerChute VM 1 on the NMC get erased. So i manually re-added all agents from VM1 plus the entries i need on VM2 and I end up with the result:

 

PowerChute VM1: all machines automatically recognized during installation still correct

NMC: all machines re-added from VM1 + the machines added for VM2

PowerChute VM2: all agents from VM1 + VM2 + even the PowerChute VM1 itself

 

with no possibility to assign the correct agents to the right PowerChuteVM.

 

Our idea now was to attach the VMware Host 1 with the PowerChute VM 1 to UPS Outlet group and the VMware Host 2 with PowerChute VM 2 to Outlet group 1, so both VMs should be able to identify its own outlet group and the VMs running on the corresponding VMware hosts.

 

I hope this was clear enough for you to understand the current conditions, so now the questions are:

 

1.Is this going to work at all?

2.Should the PowerChute VMs be able to correctly recognize the running VMs on the VMware Hosts automatically?

3.If not, is there a possible solution you can think of and which one would that be?

 

Thanks for your help

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore