Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 08:03 AM . Last Modified: 2024-03-07 10:17 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:03 AM . Last Modified: 2024-03-07 10:17 PM
I am running a Smart-UPS RT 10000 XL with a AP9617 module installed.
The output relay contacts are set up with a small 12v transformer and a strobe light in series, with one leg of the circuit through the UPS relay. so when the relay closes it completes the circuit and the strobe flashes.
Whenever an alert happens that causes the strobe to flash however I get the following message in the logs"A fault exists for integrated Environmental Monitor Output Relay".
Is this saying I am overloading the output relay or just alerting me to the fact the output relay is in operation.
The word "FAULT" scares me!
Any help appreciated!
Cheers,
-Nick
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:04 AM . Last Modified: 2024-03-07 10:17 PM
It doesn't mean there's an electrical problem. It's alerting you that the relay is not in its normal state.
A normally open relay, when closed, will signal a fault.
A normally closed relay, when opened, will signal a fault.
I hope the word "fault" didn't scare you too much! Perhaps it was a poor choice of words.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:04 AM . Last Modified: 2024-03-07 10:17 PM
It doesn't mean there's an electrical problem. It's alerting you that the relay is not in its normal state.
A normally open relay, when closed, will signal a fault.
A normally closed relay, when opened, will signal a fault.
I hope the word "fault" didn't scare you too much! Perhaps it was a poor choice of words.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:04 AM . Last Modified: 2024-03-07 10:17 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:04 AM . Last Modified: 2024-03-07 10:17 PM
Maybe rather than "fault" it could say "Integrated Environmental Monitor Output Relay has operated" and "Integrated Environmental Monitor Output Relay has reset"...?
Something for the firmware / software people to work on maybe.
Thanks for your help and clearing up the confusion.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:04 AM . Last Modified: 2024-03-07 10:17 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:04 AM . Last Modified: 2024-03-07 10:17 PM
I got SURT 5KVA and same errors, there hundreds msg sent to me everyday. Can you advise on how to stop this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:04 AM . Last Modified: 2024-03-07 10:17 PM
what model card is yours? AP9631 or AP9619? can you post your event.txt? you can follow these instructions -> http://nam-en.apc.com/app/answers/detail/a_id/9321
also, what is attached to your NMC? (probe, etc)
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.