Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

A fault exists for integrated Environmental Monitor Output Relay

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A fault exists for integrated Environmental Monitor Output Relay
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:03 AM . Last Modified: ‎2024-03-07 10:17 PM

0 Likes
4
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:03 AM . Last Modified: ‎2024-03-07 10:17 PM

A fault exists for integrated Environmental Monitor Output Relay

I am running a Smart-UPS RT 10000 XL with a AP9617 module installed.
The output relay contacts are set up with a small 12v transformer and a strobe light in series, with one leg of the circuit through the UPS relay. so when the relay closes it completes the circuit and the strobe flashes.

Whenever an alert happens that causes the strobe to flash however I get the following message in the logs"A fault exists for integrated Environmental Monitor Output Relay".

Is this saying I am overloading the output relay or just alerting me to the fact the output relay is in operation.

The word "FAULT" scares me!

Any help appreciated!

Cheers,

-Nick

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

0 Likes
0
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

It doesn't mean there's an electrical problem. It's alerting you that the relay is not in its normal state.

A normally open relay, when closed, will signal a fault.
A normally closed relay, when opened, will signal a fault.

I hope the word "fault" didn't scare you too much! Perhaps it was a poor choice of words.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

0 Likes
0
836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

It doesn't mean there's an electrical problem. It's alerting you that the relay is not in its normal state.

A normally open relay, when closed, will signal a fault.
A normally closed relay, when opened, will signal a fault.

I hope the word "fault" didn't scare you too much! Perhaps it was a poor choice of words.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

0 Likes
0
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

Maybe rather than "fault" it could say "Integrated Environmental Monitor Output Relay has operated" and "Integrated Environmental Monitor Output Relay has reset"...?

Something for the firmware / software people to work on maybe.

Thanks for your help and clearing up the confusion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

0 Likes
0
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

I got SURT 5KVA and same errors, there hundreds msg sent to me everyday. Can you advise on how to stop this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

0 Likes
0
834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:04 AM . Last Modified: ‎2024-03-07 10:17 PM

what model card is yours? AP9631 or AP9619? can you post your event.txt? you can follow these instructions -> http://nam-en.apc.com/app/answers/detail/a_id/9321

also, what is attached to your NMC? (probe, etc)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of