Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 05:15 AM . Last Modified: 2024-03-18 03:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:15 AM . Last Modified: 2024-03-18 03:40 AM
|
||||||||||||||||||||
|
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:15 AM . Last Modified: 2024-03-18 03:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:15 AM . Last Modified: 2024-03-18 03:40 AM
Hello Shanon,
Thank you very much for your response. I will apply that and let you know the result please.
APC Smart UPS - RT 10000 VA 230V, SN: QS1431270334
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:15 AM . Last Modified: 2024-03-18 03:40 AM
Hello Aka,
I do apologize for the delay in the response to your post, but these logs indicate that there is definitely an issue with your UPS. First, by the fact that it is dropping your load, but also the "backfeed relay fault", which indicates that it is unable to prevent backfeed when on battery.
Based on the logs, you probably have a next generation Smart-UPS, like the SMC, SMT or SMX.
What is the model number and serial number?
You can do what we call a "braindead and coldstart" by removing all load, unplugging the UPS, disconnecting the batteries, reconnecting, and starting (without plugging back into the wall) the UPS on battery power. This can clear any erroneous faults.
If that does not solve the issue, I would recommend that you calling tech support at 800 800-4272. If the UPS is under warranty, then they will be able to ship you a replacement. Tech support will also ask for the model and serial, so I would recommend being with the UPS and have that information ready when callings.
Thanks,
Shanon
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:15 AM . Last Modified: 2024-03-18 03:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:15 AM . Last Modified: 2024-03-18 03:40 AM
Hello Shanon,
Thank you very much for your response. I will apply that and let you know the result please.
APC Smart UPS - RT 10000 VA 230V, SN: QS1431270334