9631 SNMP Temperature Values Incorrect

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 9631 SNMP Temperature Values Incorrect
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

0 Likes
2
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

9631 SNMP Temperature Values Incorrect

The APC 9631 network management card with current firmware 5.1.7 outputs the wrong SNMP temperature values if the Temperature Scale preference (Administration> General> Preferences> Temperature Scale:) is set to Fahrenheit for web GUI Environment display.

Per the MIBs SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5 should always result in temperature display in Fahrenheit and SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6 should always result in Celsius.

When set to Celsius:

snmpwalk [hostname] -v1 -c public .1.3.6.1.4.1.318.1.1.25.1.2

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.1.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.2.1 = INTEGER: 2

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.1.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.2.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.1.1 = STRING: "Port 1 Temp 1"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.2.1 = STRING: "Port 2 Temp 2"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.1.1 = STRING: "Port 1"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.2.1 = STRING: "Port 2"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.1.1 = INTEGER: 77

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.2.1 = INTEGER: 77

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.1.1 = INTEGER: 25

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.2.1 = INTEGER: 25

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.1.1 = INTEGER: 38

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.2.1 = INTEGER: -1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.1.1 = INTEGER: 0

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.2.1 = INTEGER: 0

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.1.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.2.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.1.1 = INTEGER: 2

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.2.1 = INTEGER: 2

When set to Fahrenheit:

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.1.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.1.2.1 = INTEGER: 2

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.1.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.2.2.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.1.1 = STRING: "Port 1 Temp 1"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.3.2.1 = STRING: "Port 2 Temp 2"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.1.1 = STRING: "Port 1"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.4.2.1 = STRING: "Port 2"

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.1.1 = INTEGER: 171

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.5.2.1 = INTEGER: 172

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.1.1 = INTEGER: 77

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.2.1 = INTEGER: 78

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.1.1 = INTEGER: 38

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.7.2.1 = INTEGER: -1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.1.1 = INTEGER: 0

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.8.2.1 = INTEGER: 0

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.1.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.9.2.1 = INTEGER: 1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.1.1 = INTEGER: 2

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.10.2.1 = INTEGER: 2


Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 9631
  • management
  • network_management_card
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

we had an issue with this but it was fixed already over a year ago where a double calculation was being performed depending on the preference setting. I know you said this was version 5.1.7 firmware but can you please provide a screenshot of the firmware versions from the web interface under Administration->General->About please.

I just double checked this on my end for sanity's sake knowing it was a non issue these days and verified my temp preference was on Celsius and I am seeing 82 for uioSensorStatusTemperatureDegF and 28 for uioSensorStatusTemperatureDegC as I expect to.

Here is what I am running per sysDescr (.1.3.6.1.2.1.1.1) OID under mib-2 which maybe you can get that instead for me: APC Web/SNMP Management Card (MB:v4.0.1 PF:v5.1.7 PN:apc_hw05_aos_517.bin AF1:v5.1.7 AN1:apc_hw05_sumx_517.bin MN:AP9631 HR:05 SN: BA08XXXXXXX MD:01/16/2009) (Embedded PowerNet SNMP Agent SW v2.2 compatible)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

we had an issue with this but it was fixed already over a year ago where a double calculation was being performed depending on the preference setting. I know you said this was version 5.1.7 firmware but can you please provide a screenshot of the firmware versions from the web interface under Administration->General->About please.

I just double checked this on my end for sanity's sake knowing it was a non issue these days and verified my temp preference was on Celsius and I am seeing 82 for uioSensorStatusTemperatureDegF and 28 for uioSensorStatusTemperatureDegC as I expect to.

Here is what I am running per sysDescr (.1.3.6.1.2.1.1.1) OID under mib-2 which maybe you can get that instead for me: APC Web/SNMP Management Card (MB:v4.0.1 PF:v5.1.7 PN:apc_hw05_aos_517.bin AF1:v5.1.7 AN1:apc_hw05_sumx_517.bin MN:AP9631 HR:05 SN: BA08XXXXXXX MD:01/16/2009) (Embedded PowerNet SNMP Agent SW v2.2 compatible)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:13 AM . Last Modified: ‎2024-03-05 11:06 PM

My bad - of the many, MANY smart-UPS' that we are monitoring, the ones with the problem are NOT running 5.1.7.  I inadvertently checked firmware on 3 that were not having the problem.  Thanks much.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore